I think T stands for load, don't know why the letter T though, maybe some old latin thingie
 
T stands for terminal. You normally see it on the output side of the contactor as on the outgoing side the phases can be connected to the motor in a different sequence than L1 L2 L3 say if you want it to run in a different direction but on the incoming side it should be connected in the correct phase sequence.
 