The plastered in, crimped joints in heat shrink sleeve, argument has been a failed defence in at least two court cases resulting from electrical accidents.
All you guys that are heat shrink sleeving crimped joints and then plastering over, seem to have forgotten about:
526.5 Every termination and joint in a live conductor or PEN conductor shall be made within one of the following or a combination thereof:
i) A suitable accessory complying with the appropriate product standard.
ii) An equipment enclosure complying with the appropriate product standard.
iii) An enclosure partially formed or completed with building material which is non-combustible when tested to BS476-4
Specifically 526.5 (iii) an enclosure can be PARTIALLY formed or COMPLETED with non-combustible building material tested to BS 476-4. The enclosure CANNOT therefore be made totally from building material.
The most common infringement of this is a crimped termination, covered with supplementary insulation (e.g. heat-shrink sleeve) and buried directly in the wall with building material (e.g. plaster).
Any type of tape or sleeving used in addition to basic insulation, is defined as supplementary insulation, even if it completely encloses the termination it is NOT an enclosure.
Any cable conductors covered with supplementary insulation, to effectively recreate the double insulation of the original cable, needs to be at least equivalent to that of the original cable product standard and would require impulse dielectric strength testing to confirm this. The cable product standards do not specify an impulse withstand capability. However, 412.2.4.1, Note 1, tells us that cable insulation must be at least equivalent to requirements of BS EN 61140 for reinforced insulation, which does specify impulse withstand capability.
All you guys that are heat shrink sleeving crimped joints and then plastering over, seem to have forgotten about:
526.5 Every termination and joint in a live conductor or PEN conductor shall be made within one of the following or a combination thereof:
i) A suitable accessory complying with the appropriate product standard.
ii) An equipment enclosure complying with the appropriate product standard.
iii) An enclosure partially formed or completed with building material which is non-combustible when tested to BS476-4
Specifically 526.5 (iii) an enclosure can be PARTIALLY formed or COMPLETED with non-combustible building material tested to BS 476-4. The enclosure CANNOT therefore be made totally from building material.
The most common infringement of this is a crimped termination, covered with supplementary insulation (e.g. heat-shrink sleeve) and buried directly in the wall with building material (e.g. plaster).
Any type of tape or sleeving used in addition to basic insulation, is defined as supplementary insulation, even if it completely encloses the termination it is NOT an enclosure.
Any cable conductors covered with supplementary insulation, to effectively recreate the double insulation of the original cable, needs to be at least equivalent to that of the original cable product standard and would require impulse dielectric strength testing to confirm this. The cable product standards do not specify an impulse withstand capability. However, 412.2.4.1, Note 1, tells us that cable insulation must be at least equivalent to requirements of BS EN 61140 for reinforced insulation, which does specify impulse withstand capability.
Last edited by a moderator: