Why do you need to buy that specific blank??? When you buy wylex, Crabtree, square d they all come with simple clip in blanks surely they meet the regs
He is referring to the type that sit on the din rail not the push fit blanks see belowQ1.59
Do blanks fitted in a distribution board or consumer unit that can be removed without the use of a tool or key comply with the requirements of BS 7671 with regard to access to live parts?
If the distribution board or consumer unit is fitted with blanks that can be removed without the use of a tool or key resulting in live parts being made accessible to touch, at least one of the following requirements must be complied with (in addition to the manufacturer’s instructions):
The lid over the blanks can be secured and opened only by use of a tool or key
The distribution board or consumer unit is in a locked location accessible only by key held by a responsible person
The distribution board or consumer unit is located in a generally inaccessible area (in which case compliance with other relevant requirements (such as accessibility for operation, maintenance and repair) needs to be confirmed)
If the distribution board or consumer unit is located in a generally accessible area and has a flap-type lid with no securing device, the blanks fitted must be of a type that can be removed only by opening the front cover, using a tool or key.
Regulation number(s) 134.1.1 416.2.3 416.2.4
Taken from the ESC website