One of my guys has found a DB in an under stairs toilet mounted 200mm away from the sink and is not 100% on the code. I am quite comfortable for him to C2 it but I'm really struggling here to find a bomb proof regulation to back that up, I must be missing one that is blindingly obvious. Any thoughts?
 
Water ingress is the most immediate danger so maybe

512.2 suitability of equipment for external influence ?
416.2 if the enclosure has had it's IP rating compromised by cable entries ?

Neither of those feel like the watertight (excuse the pun) reg you are looking for though.
 
Difficult one im afraid Mr.Skelton - as you say theres no set in stone regulation, so some people would argue no-code and just a note on the cert. Afterall the 300mm for accessories near sinks and hobs is just a guideline.

As Andy has said, 512.2 is about all you can go on.
 
I agree guys, I had 512.2 in mind but was trying to find something more solid to back it up. It would help if the 300mm was reg not advice lol. I just have to play the gut feeling card and apply common sense. A DB no more than a hands span away from a sink is bad news IMHO. C2 and 512.2 it is then. Cheers fellas.
 
I remember a similar thread last year and the consensus was it's no code because the usual bathroom zones don't apply to handwash sinks so unless there was an update in the regs I think you'd be hard pushed to justify C2 if anyone queries it.
 