Hey was wondering your views on this mains “relocation I came across” it’s the old steel wire mains run in conduit with the conduit being the main earth coming from a 80amp fused switch near the cut out. I have told the client that I would need to run a new supply cable due to the earth being connected from the conduit using a bonding clap (which was lose when i first inspected it). Also on the circuits coming out of the relocated DB is a lighting circuit run in the old valconies rubber with no cpc which I have also said would need to be replaced due to it being run through a wooden roof(church roof). What surprised me is they have only have an inspection done a few weeks ago and all this was passed. Any ideas on why they have passed it ? Thanks