UK Db change and ECIR

Hey was wondering your views on this mains “relocation I came across” it’s the old steel wire mains run in conduit with the conduit being the main earth coming from a 80amp fused switch near the cut out. I have told the client that I would need to run a new supply cable due to the earth being connected from the conduit using a bonding clap (which was lose when i first inspected it). Also on the circuits coming out of the relocated DB is a lighting circuit run in the old valconies rubber with no cpc which I have also said would need to be replaced due to it being run through a wooden roof(church roof). What surprised me is they have only have an inspection done a few weeks ago and all this was passed. Any ideas on why they have passed it ? Thanks

IMG_0893.jpeg
 
I think he means the old braided cable that looks silver, rather than brass coloured copper.

Confused with steel wire ARMOUR, which of course is completely different.


It was passed recently probably because it was done “on the cheap” by someone that didn’t take enough time.
 
I think you mean tinned copper.
Looking at your picture that is well beyond it's expected service life. Before I undertook this work I would give it a thorough inspection and test throughout.
 