Could any one please tell me what I'm missing and how did they calculate that ....
 

Attachments

  • 2016-06-08_23.17.58.jpg
    2016-06-08_23.17.58.jpg
    130.2 KB · Views: 90
can't see it pic too small.
 
It's saying :
You have indicated demand load 23kva per flat , which is rather high for gas heated property. Generally load of 2-3 kva is adequate for gas heated domestic property

Kind regards
UK power networks
 
just opened your pic . in a prog. i have so i could see the print. obviously, 23kVA is silly for a gas heated flat. add up the \in ratings of the MCBs in the CU and divide by 3. a sensible demand would be about 5kVA.
 
for demand, you have to consider an average usage. showers are only on for maybe 15 minutes at a time. hobs, whether induction or nor, have their own diversity allowed for as the loads cycle on/off due to the thermostats, so, foir example, a 12kW hob would only draw about 20A on average.
 
So if they assuming 2-3 kva what size of primary overcurrent would they use ???
So I basically calculating peak not demand ....
 
You should be assessing the likely current draw on the supply on a regular basis over time.

The 2-3 kVA from UKPN is their usual assessment of a domestic property for which they would usually supply a 60A main fuse (for a flat).

If you have a high power electric shower and a large cooker then your demand would increase somewhat and it may be that your are nearer 6 kVA and you may need an 80A main fuse to handle the load plus shower safely, even thought a 60A will not go it can get weakened.
 