Does anyone have a deta 20a mcb 6 or 10k. I’ve got a faulty 20a mcb that I’d like to replace so I don’t have to do anything more involved to split a ring main with open neutral end to end continuity.
It’s an old er version where the switch is black and the busbar splits around the bottom terminal screw.
I’m willing to if to pay if some one does.
Thanks
 
It’s an older version where the switch is black and the busbar splits around the bottom terminal screw. Picture attached
 

Attachments

  • IMG_5787.jpeg
    IMG_5787.jpeg
    2 MB · Views: 315
I seem to think I might have some of these, but can’t remember what size. Will they have to be 20A, or would the circuit be ok on a 16?
 
Ok… I’ve had a look in store, and I’ve got everything but Deta.

Anyone need an old MK, MK Sentry, proteus, M2, MEM/ Eaton, Wylex, Hager, BG…..
 
Help!
Does anyone have a deta 20a mcb 6 or 10k. I’ve got a faulty 20a mcb that I’d like to replace so I don’t have to do anything more involved to split a ring main with open neutral end to end continuity.
It’s an old er version where the switch is black and the busbar splits around the bottom terminal screw.
I’m willing to if to pay if some one does.
Thanks
Ebay has them but 20 amp is out of stock .would a 16 amp do
 
Help!
Does anyone have a deta 20a mcb 6 or 10k. I’ve got a faulty 20a mcb that I’d like to replace so I don’t have to do anything more involved to split a ring main with open neutral end to end continuity.
It’s an old er version where the switch is black and the busbar splits around the bottom terminal screw.
I’m willing to if to pay if some one does.
Thanks
Is it the kitchen ring that's broken I can see a 16 in for kitchen sockets ,has it been made into 2 radials.
 
Ok… I’ve had a look in store, and I’ve got everything but Deta.

Anyone need an old MK, MK Sentry, proteus, M2, MEM/ Eaton, Wylex, Hager, BG…..
Thank you for trying
 
Is it the kitchen ring that's broken I can see a 16 in for kitchen sockets ,has it been made into 2 radials.
Currently two radials in the one 16a mcb whilst I wait for another 16 from eBay or preferably a 20. The broken neutral end to end can’t be found in any sockets or jb’s on the kitchen ring.
 
Currently two radials in the one 16a mcb whilst I wait for another 16 from eBay or preferably a 20. The broken neutral end to end can’t be found in any sockets or jb’s on the kitchen ring.

Currently two radials in the one 16a mcb whilst I wait for another 16 from eBay or preferably a 20. The broken neutral end to end can’t be found in any sockets or jb’s on the kitchen ring.
20 amp mcbs will be in short demand prob for that very reason
 
Currently two radials in the one 16a mcb whilst I wait for another 16 from eBay or preferably a 20. The broken neutral end to end can’t be found in any sockets or jb’s on the kitchen ring.
Out of interest, if you don't know where the N break is, how are you deciding where you split the live?
 
Out of interest, if you don't know where the N break is, how are you deciding where you split the live?
I don't think the live is being split by the sounds of it
 
Not only must the live be split, but the neutrals must be disconnected as well, at the sockets on the RFC either side of the break.
 
I hope that's not the case, or that professionals are assisting in it?

I hope that's not the case, or that professionals are assisting in

Not only must the live be split, but the neutrals must be disconnected as well, at the sockets on the RFC either side of the break.
I changed an oldd rewirable wylex fuse board where someone had written on the front of a 30 am fuse holder "15 amp only " needless to say it was a 30 amp wire that was in as it was the only socket circuit in flat .(the live had popped out the cookerhood switch)makes you wonder why the regs don't do something about rewireable fuses.a leased tenant can easily upgrade a fuse wire to any size by nipping down to local shop but they can't change an mcb or are very very unlikely to do so.ive seen a 5 amp fuse wire been wrapped around the terminals several times because its so fiddely and someone has lost the rag .
 
I changed an oldd rewirable wylex fuse board where someone had written on the front of a 30 am fuse holder "15 amp only " needless to say it was a 30 amp wire that was in as it was the only socket circuit in flat .(the live had popped out the cookerhood switch)makes you wonder why the regs don't do something about rewireable fuses.a leased tenant can easily upgrade a fuse wire to any size by nipping down to local shop but they can't change an mcb or are very very unlikely to do so.ive seen a 5 amp fuse wire been wrapped around the terminals several times because its so fiddely and someone has lost the rag .

Never underestimate the power of stupid

IMG_20220919_101339056_HDR.jpg
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Cornwall
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Deta 20a mcb
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Thread Tags

Advert

Thread statistics

Created
Cas james,
Last reply from
Jock from the north,
Replies
19
Views
643

Advert