Disconecting 3PH+N cable

Hello all,

Hope everyone is keeping well.

Quick question, a little embarrassed asking, as I'm a registered electrical contractor, but don't have a whole lot of experience with 3 phase. I've isolated a supply to a sub distribution board (see pic), but I need to now disconnect that supply cable at main breaker in switch room.

The cable comes through a cable cubicle and into the outgoing side of breaker. Ive tested to be sure it's de-energised, but the incoming side will be live. I don't have the option of isolating incoming side obviously.

My question is, is there need to worry about an arc fault radius when I disconnect the outgoing cable from the main switch or is it relatively safe? See photos attached.

Thanks
1000108102.jpg
1000108101.jpg
 
60947-2 devices in general are deemed to provide isolation and that one would fall into that category. To be 100% check the incoming neutral does not have potential to earth as that is not isolated by the MCCB.
 