Hi. I'm currently doing my design project and have submitted the first draught I've managed to correct most of my feedback but am struggling with question 5, Determine, for one of the fridges the minimum possible CSA area of CPC which will satisfy the requirements disconnection as ads under earth fault conditions and the adiabatic equation as reg 543.1.3. The feedback I received for my first attempt was suggestive of thermal constraints and that it talks about ADS remember it's 16A *5 80A. How do I go about this as I always seem to go back to my original answer? Thanks
 
Hi. I'm currently doing my design project and have submitted the first draught I've managed to correct most of my feedback but am struggling with question 5, Determine, for one of the fridges the minimum possible CSA area of CPC which will satisfy the requirements disconnection as ads under earth fault conditions and the adiabatic equation as reg 543.1.3. The feedback I received for my first attempt was suggestive of thermal constraints and that it talks about ADS remember it's 16A *5 80A. How do I go about this as I always seem to go back to my original answer? Thanks
This is telling you to run the adiabatic equation in Part 5 (Selecting conductor CSA - S = √(I2t)/ k) and not the one from Part 4 (Thermal Withstand - t = k2s2 / I2). You can run thr part 4 equation but you'll already know what disconnection times you'll need to hit.

If your sizes work out then the last check is I2t < K2S2 - Is thr energy let through WITHIN (or less than) the total energy that thr conductor will take before degrading.

Don't forget to add statements to the fact at each part of the equation;

"I believe % under reg # is met because" (or the inverse; is NOT met because)

For % substitute the part of the process; coordination, volt drop, thermal withstand, conductor sizing etc)

For # substitute the regulation number that applies.

Where you're saying the design is not compliant then you need to offer resolutions (bigger cable/OCPD), bonus points for mentioning consideration for Appendix 17 and consideration of potential saving in energy efficiency vs outlay
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Readytorum

Trainee
Joined
Location
daventry
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Disconnection under ADS
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
1

Thread Tags

Advert

Thread statistics

Created
Readytorum,
Last reply from
Lister1987,
Replies
1
Views
147

Advert

Back
Top