Thanks to everyone who replied yesterday.

Quick Update: Spoke to NIC tech help today. The chap I spoke to suggested that I protect the sub main cable with a time delay 100mA RCD in order to maintain discrimination with the downstream RCDs. But that this is a departure and must be noted as such. Also, that it would be a good idea to provide a risk assessment to identify the risk of the potentially buried cable without a 30mAmp (additional protection).

Also to note within the risk assessment that I am in fact improving the overall safety of the installation and not making it less safe than it already is.

Will update again once I've spoken to client

Cheers again
 
It is an interesting choice for the NICEEIC to make, the regulations specifically state that any departure from the regulations, that may be noted on the electrical installation certificate, may not provide any less safety than that provided by compliance with the regulations.
This is not the case in this instance and should not be considered to be complying with the regulations or as an acceptable departure.

However in practical terms increasing the safety of the installation is of benefit and it could be considered that increasing the safety could be undertaken even in contravention of the regulations as otherwise you are retaining a more dangerous state. But that is a decision for the electrician on site to make as a call on a case by case basis.
 
If the NICEIC are happy for that, I would request it in writing from them so that should the brown stuff hit the fan they will be stood along side you in court.
 