The maximum derating of cables in loft insulation is 50%, so if the load will comfortably never cause the cables to be subjected to that current (or even better, if the MCB is suitably chosen so as to limit the current appropriately), then I don't see the point of noting it on your PIR. Up to you though... As has already been said; if you really want to protect yourself, note it.
Noting it is somewhat academic anyway if you go on to change the board, since then you should either select MCBs to suit the cable installation method(s), or, if you need to drive higher load(s) than the cable/ref method(s) can handle, you'll need to make provision for the cable(s) to take the load, either by seperating them from the insulation, or increasing their csa.