Whats the crack with non fire rated down lighters? do i have to insist they are changed for fire rated or hoods added or is it purely just a recommendation?
 
fire rated downlights are only required when the ceiling in which they are fitted is a fire barrier. this is usually only the case when the floor above is separate occupancy flats, etc.) or an intgral garage with living accom. above ( in domestic situations)
 
So if the down lighters are in a kitchen with a bedroom above this is acceptable?
 
perfectly. the fire rated fittings are to reinstate the integrity of a fire barrier ceiling, not to stop the fitting from catching fire, but to prevent a fire in , say, the lower room, spreading to the upper room. in a single occupancy dwelling, ceilings are not fire barriers.
 
quote_icon.png
Originally Posted by Moses
No, you need fire rated ones.



sorry, moses. i disagree. see my post #5

Read more: http://www.electriciansforums.net/e...-forum/58321-down-lighters.html#ixzz1x8RjXA00

Key?
:wazzzup:​
 
To be quite honest, fire rated down lighters are so cheap now i fit them as standard, don't care what the Regs are.
 
well, i dispute that. for a start, where in the doc. does it even mention ground floor ceilings?????
 
well, i dispute that. for a start, where in the doc. does it even mention ground floor ceilings?????

Two Storey
House
Ceiling below roof None C2, L1, and P1
First floor 30 minutes * B3, E2, L1, and
P1



First "floor" is = Ground floor ceiling
Ceiling below roof = First floor ceiling
 