what type of flex do you guys use for downlighter wiring, obviously just from the loop in, loop out JB, down to the fitting, now i know it will have to be high temperature/ heat resistant but what would the cable code be to look for in the catalogues,

thanks
 
Does anyone bother with using flex on the fittings that allow 2 T&Es to loop in and out, such as the Click Flameguards.
 
I've never seen a manufacturer request it to be wired in flex. And I don't really see the need if it's a decent fitting designed to be wired into. As your just putting a unnecessary joint in. If you had to have jbs above each light I would probably use flex. I just think its easier and better to limit jbs.
 
I'm just doing a kitchen where the ceiling void has underfloor heating in it as well, so it's heat flex all the way from the switch onwards.
 
I've seen too many examples of T+E burnt out against downlighter body for my liking. So IMHO it's T+E to Ashley 501 JB (or similar 17th ed compliant JB) then heat resistant flex to downlighter.
 
I know what you mean have come across it. But surely If the cable is secured correctly it shouldn't be touching the side of the fitting lol
 
I know what you mean have come across it. But surely If the cable is secured correctly it shouldn't be touching the side of the fitting lol

True, but I still think it's best practice.
Whereabouts in Cornwall are you?
 
Last edited by a moderator:
i used 500mm of heat resistant for each downlight but i have also just wired whole circuit in flex..
 