Good morning, im doing some revision on tt systems for 2391. From my understanding regs say double pole isolation of a TT system is required, and this can be from the main switch of the dist board or CU. Regs also say (rcd or) rcbo protection for all final circuits is necessary and single pole devices can be used.

However, its often recommended (although not a regulation for TT systems) to fit double pole rcbo’s for final circuits – why is this? Is it to minimise danger in the event of an open neutral at supply, and/or diverted neutral currents, together with a neutral-earth fault, which could lead to dangerous touch voltages on earthed parts?

Similarly, in special locations like caravan parks - marinas – fair grounds ect where double pole RCD protection for all final circuits IS required, is it for the same reasons? and deemed necessary as the risk is more likely in these environments? Thanks
 
For purposes of isolation the neutral must be disconnected for a TT system as unlike a TN system it is not deemed to be at earth potential. Circuit protection does not need to be double pole (consider if fuses are still in use). The reason double pole protective devices are sometimes used is if there is an upfront RCD installed to prevent nuisance tripping of that device from a neutral fault on one of the circuits it covers, for example you have a neutral fault to earth on a circuit, isolation of the RCBO for that circuit does not prevent the upfront RCD detecting that fault but a double pole device would.
 
Last edited:
For purposes of isolation the neutral must be disconnected for a TT system as unlike a TN system it is not deemed to be at earth potential. Circuit protection does not need to be double pole (consider if fuses are still in use). The reason double pole protective devices are sometimes used is if there is an upfront RCD installed to prevent nuisance tripping of that device from a neutral fault on one of the circuits it covers, for example you have a neutral fault to earth on a circuit isolation of the RCBO for that circuit does not prevent the upfront RCD detecting that fault but a double pole device would.

Have you ever come across dangerous N-E potential on a TT @westward? I mean when everything is functioning normally, no faults etc.
Would you definitely be inclined to switch off the main switch when working in a property which has a TT, rather than just isolating the circuit on an MCB or single pole RCBO?
 
Have you ever come across dangerous N-E potential on a TT @westward? I mean when everything is functioning normally, no faults etc.
Would you definitely be inclined to switch off the main switch when working in a property which has a TT, rather than just isolating the circuit on an MCB or single pole RCBO?
It would be wise to check the potential difference between neutral and earth on a TT system prior to undertaking any works and I would also disconnect the neutral conductor for that circuit if the protective device was single pole and I could not isolate the distribution board.
 
Double pole isolation on indivitual circuits (e.g. RCBOs with swithced neutrals) on TT systems is a good idea to minimise disruption. As you say, the double pole main switch can be used for safe isolation, but it would be nice if you could safely isolate the lighting circuit while you changed a light fitting, without turning off the internet and boiler, wouldn't it?

For caravans, marinas, fairgrounds etc, there is an increased risk of incorrect polarity (L <-> N) on the supply cable linking the supply to the caravan / boat / ride to the source of supply; also, in other countries, supply polarity is less formally enforced, so having double pole protective devices on your vehicle / boat / ride reduces the shock risk if what you think is N is actually L, because the source supply isn't wired up the way you expect it to be.
 
Thanks @ Happysteve, My assuming that Caravan Parks, Marina's and Fair grounds would be at higher risk from broken PEN and other neutral issues is a non starter as no PME allowed on those sites :tired: anyway. And as you mention yes now I see how reverse polarity would be increased risk in those environments due to our international cousins using their own leads/cabling ect. Cheers
 