Earth rod

I have had an eicr carried out on an Edwardian ex rental property that i am about to sell. Doing some work outside the property, i came across a very rusty old iron pin, approx 6mm dia, with a pointed top. I hammered it down below ground level, where i was laying slabs. Could this possibly be the property's earth rod? The electrian who carried out the eicr said that house had a strong earth. Am i concerning myself unnecessarily?
 
I have had an eicr carried out on an Edwardian ex rental property that i am about to sell. Doing some work outside the property, i came across a very rusty old iron pin, approx 6mm dia, with a pointed top. I hammered it down below ground level, where i was laying slabs. Could this possibly be the property's earth rod? The electrian who carried out the eicr said that house had a strong earth. Am i concerning myself unnecessarily?
Could be an earth for early radio's that the house may have seen, or even for the telephone!
If you have the EICR handy, can you reply with which earthing arrangement has been ticked - see below.
Your form probably won't look exactly like this, but the code letters should be the same.

IMG_1330.jpeg
 
I have had an eicr carried out on an Edwardian ex rental property that i am about to sell. Doing some work outside the property, i came across a very rusty old iron pin, approx 6mm dia, with a pointed top. I hammered it down below ground level, where i was laying slabs. Could this possibly be the property's earth rod? The electrian who carried out the eicr said that house had a strong earth. Am i concerning myself unnecessarily?
Did this have any cable attached to it.
 
Could be an earth for early radio's that the house may have seen, or even for the telephone!
If you have the EICR handy, can you reply with which earthing arrangement has been ticked - see below.
Your form probably won't look exactly like this, but the code letters should be the same.

View attachment 124620
TT ticked. Earth rod location under floor. Resistance to earth 0.66. Method of measurement E3 (earth loop tester). Does this mean anything to you. I'm not sure how he would know if the earth rod was under the floor. At the time he asked about it, but as his reading was so high he didn't say anything more. I gave him the previous cert, so maybe he used that info. When he asked about the location of the earth, i said i didn't know. From the previous cert, which i gave to him, it said the inspector didn't know where it was but put it as
underneath the comsumer unit. The rusty pin that i found, i just tapped down about 2" so it wasn't in my way. It was about 1.5m, away from the consumer unit. Does any of this help?
 
Does any of this help?
Well, it confirms your installation should have an earth rod somewhere, which you knew, but I was a bit unclear!
I would expect to see a cable connected to the top of the rod you found, if it was the installation earth. It would also likely be made of copper, or copper plated steel, not iron, not typically have a pointy top but a clamp to which the earth cable is connected, and you'd probably have to whack it quite hard, not 'tap' it, to move it.

The low resistance of 0.66 ohms is very good for a TT system in my limited experience. You called it 'high' but I assume you really meant 'good' as per the electrician's comment.

If the electrician saw the earth conductor going down the wall under the consumer unit, could he have lifted a floor board or similar to find the rod, or would floor coverings etc not allow that?

If you're concerned because the rod was knocked in after the EICR was done, I guess one way to be certain all is OK, would be to have just the Earth Loop test repeated!
 
Ring the electrician and ask him where the earth rod was.
If he couldn't find it, then that should have gone down as an FI (Further Investigation), and I would personally have classed the installation as unsatisfactory and let you know we need to find it, or install a new one.
 
@Stevec1999
What does 'earth rod location under floor ' mean?
I'm guessing it means they have guessed that it is under the floor and not accessible.
We can't guess. They just have to put FI, and either find it at extra cost or install a new one. You absolutely have to be able to get to the this rod as it will have a screwed connection on it holding your Main earth cable in place. This is a vital part of your electrical system. This is not me being over cautious, it simply has to be done.

I suspect you will need a new earth rod put in. Very, very rough idea of cost £100 - £300. Depending vastly on the location of you consumer unit.

Don't just leave it and think 'well everything is working fine'. It's like driving around in a battered old car with no breaks, thinking everything is fine, until you need to break.

Also, the 'strong earth' is very likely to be due to other cables attached to your gas or water pipes. These cannot (and are not allowed to) be relied upon, as at some point they may well get changed to plastic
 