In my house the mains cable is steel wire armoured and have live and neutral but no earth wire. I had national grid and they said it my responsibility to provide earth and if they have to fix the charge is approx £160.00. I said it is your responsibility to provide earth. They said it was done by mem. There is a clamp on the steel wire with 6mms earth cable and this is not correct size.
Whose responsibility it to supply the earth conductor
Your answer would be appreciated also is it safe as it is with no earth.
Thank you all
 
In my house the mains cable is steel wire armoured and have live and neutral but no earth wire. I had national grid and they said it my responsibility to provide earth and if they have to fix the charge is approx £160.00. I said it is your responsibility to provide earth. They said it was done by mem. There is a clamp on the steel wire with 6mms earth cable and this is not correct size.
Whose responsibility it to supply the earth conductor
Your answer would be appreciated also is it safe as it is with no earth.
Thank you all
If the supply is TT then it is the home owners responsibility to prove an earth (Earth Electrode).
If TN-S (as sounds like you describe) the responsibility is the DNO's upto the MET (Main Earthing Terminal). The size of this is determined by the DNO and often smaller than a 16mm required by regs between the CU and the MET.
 
has anyone seen the photo in my last message I posted. the nat grid wants £164.16 to provide earh earth. This is their problem or
is it my problem as i live in semi detached house on the main road. there are 40 houses on the road. your advise would be appreciated
thank you
 
A load of posts have disappeared because I did reply about this. Will do it again at some point.
 
I'm not too sure what the problem is? There is what looks like a 6mm clamped on to the supply, TNS.
We may not like or ever use 6mm for a main earth but I suspect the DNO still class it as fine.
Happy to be educated though.
 
If the DNO provided that earth terminal they are obliged to maintain it but looking at it I suspect they did not. They are obliged to ensure the service head and cable sheath are effectively earthed which causes problems if you put in place a TT system as you may have different earthing systems in close proximity. If it were me I would pay the £160.
 
Electrictity supply and quality regs state they must maintain a tns, which this is. just mention ofgem to them. its a cast iron head on a pilc, they should change it. mention the lights flicker and you can hear arcing, they will change the head
 