Dave Fone

We are working on a job where the incoming supplies two cables,live and neutral enter the service head.The neutral is fused and there is no dedicated earth point.
We need to instal a new pump and obviously require an earth.
Is it acceptable to now run an earth from the fused neutral point which know becomes a TN-C-S system rather then a T-N-S system.
 
Hey Dave.

I would say definately not.

How is the system earthed at the moment??

It sounds like that is a TT system and there should be an earth electrode somewhere.

The only people that can give you a TN-C-S system are the DNO you cant make one yourself because you dont know wether or not the neutral is spiked down along the line or not.

Worth a phone call to DNO methinks.

Cheers.
 
The visual checks are that the service head is feed from a joint that has been crutched onto a mains feeder.
I would guess that the outer sheathing of the feeder cable is the CPC.
Not to sure if an earth electrode is used as there is no sign at all of an earth cable.

Any ideas?????
 
Hey.

Seems strange that.

Have you taken a Ze reading?? this may give you an indication of what type of earthing system you have.

Are there any D.B's you can open up to see if there is an MEC in there somewhere.

Is it a new service head??

Deffo worth contacting your DNO to find out what the score is.

Cheers.
 
The service head is about 1970`s ish and there was lighting and power connected to it via a consumer unit.
Like I said no earth but only live / neutral.

Any suggetions
 
If the N is fused, then it is beyond normal (it does happen in certain situations) ...but very unlikely in the case you mention.

I would convert it to conventional and bridge the neutral, but you may need to check that all feeds in the installation are not switching neutrals, rather than line. It could well be you have neutrals switched rather than live ...a mine field if a big installation.

I have seen it before, we were lucky in that all switches were double pole
 
Hey.

Ring the DNO and explain that you have on old cut-out with a fused neutral and that you'd like it changed as it is now unsafe.

If there are no other obvious signs of a main earth then I would definately install an earth rod.

Cheers.
 

Reply to earthing in the Australia area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
622
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock