Ive been asked to have a look at a remedial work quotation provided by a company and I'm confused at a couple of things they have brought up.
1st thing is there are 3 circuits that have "no continuity of ring final conductors" fair enough...2 of the circuits are classed as C2 and one as FI.
would the C2 faults be no continuity of the cpc and the FI is a live or neutral fault ?

and the installations are 5/6 years old this is the first eicr since the initial inspection.
another C2 fault they have said is an over rated mcb Its the original mcb that passed the first inspection

anyone shed any light on this

Ta
 
FI is Further Inspection... so they know there's an issue, but didnt have the time or scope to find where the problem was... That's down to you.

The C2's were maybe straightforward no continuity... but that could mean all of the 3 conductors, live, neutral and cpc...
The FI might be that one conductor has no continuity, but the others do... meaning you will have to search for it.
 
More information on the circuit and load would be needed.
The remedial works quote has not stated any info on the over rated circuit or load ,just that its over rated.The quote was issued by one of those companies that "do everything"
the blurb from their website is
"is a leading UK provider of electrical and fire safety testing and remedial services. Stay compliant and protected, contact us today."
I'll try and get more info,
 
You need to see it so you have some idea of the scale of the circuits and the environment they are in.
You need to see it so you have some idea of the scale of the circuits and the environment they are in.
quick update on all this...
the c2's and FI all pertain to ring circuits and they all have grid switches with 4 or more switches on them so a lot of cables going on behind them,they are also in a kitchen base unit ..at the back ,probably a loose cable in one of these.
the over rated mcb is a 30a with only one 2.5mm cable coming from it feeding a shower pump.No idea why its passed the previous EICR's
 
I remember doing some new build tests about ten years ago and there were lots of open continuity faults on the ring finals, nearly every one was at the grid switches.
 