electric shower wiring

Ive been contacted by a friend who inspects rental properties before they are let and he has said that the landlord has an electric shower which has the supply cable running in trunking round the hallway and into the bathroom,it runs behind the cistern and then through the shower door frame and up the tiled wall to the final shower position.
Ive been away from the trade for a long time but surely that's not right or do you get waterproof trunking now ?
 
I'm assuming the cable is twin and earth? I don't think this is non-compliant. Table C1 in the OSG offers this for T+E (have edited out irrelevant info):


Uses:
For general indoor use in dry or damp locations.
...
For use on exterior surface walls, boundary walls and the like.
For use as overhead wiring between buildings.
...

Comments:
...
Not recommended for underground ducts liable to become wet as unsuitable for that environment.



From the above, I infer that T+E is okay with getting temporarily wet by, for example, being rained on, but doesn't tolerate being continuously wet or submerged, as you might expect in some underground ducts. I'd have thought this would be okay in the situation you have described.
 
I'm assuming the cable is twin and earth? I don't think this is non-compliant. Table C1 in the OSG offers this for T+E (have edited out irrelevant info):


Uses:
For general indoor use in dry or damp locations.
...
For use on exterior surface walls, boundary walls and the like.
For use as overhead wiring between buildings.
...

Comments:
...
Not recommended for underground ducts liable to become wet as unsuitable for that environment.



From the above, I infer that T+E is okay with getting temporarily wet by, for example, being rained on, but doesn't tolerate being continuously wet or submerged, as you might expect in some underground ducts. I'd have thought this would be okay in the situation you have described.
Ive had a trawl over the internet and in general what you say is correct, just seems wrong to me,if i could work out how to post pictures I would have posted a couple,the installation is not very tidy,lot of silicone ,badly cut angles on the trunking,sharp edges when it passes through the shower frame,however as you say its permissible
 
Screenshot_20251022_222624_Chrome.jpg
 
Ive had a trawl over the internet and in general what you say is correct, just seems wrong to me,if i could work out how to post pictures I would have posted a couple,the installation is not very tidy,lot of silicone ,badly cut angles on the trunking,sharp edges when it passes through the shower frame,however as you say its permissible
Was going to say I bet it looks rank!
 
From #2, I didn’t think t&e was suitable for outside runs?

Trunking will be waterproof if you gum up the lid with silicone… looks awful though.

Most standard showers come with a handy trunking sized cutout on the top or bottom for cable entry.
 
From #2, I didn’t think t&e was suitable for outside runs?
Without straying too far from the OP, the same table says "Protection from direct sunlight may be necessary. Black sheath colour is better for cables exposed to sunlight.". It gives mixed messages, which is probably why some consider it okay, and others not. From my experience, the outer sheath of T+E seems to take a very long time to significantly deteriorate outdoors, certainly longer than 20 years.
 
From #2, I didn’t think t&e was suitable for outside runs?

It is but you have to factor direct sunlight and protect accordingly. If you consider that 3 faces of a building can get direct sunlight you are pretty much limited to the north facing parts of the building and ideally it is better to use a black sheath.

Was quite surprised black was better because it absorbs UV rays but I guess absorbing them is a better blocker?
 
It is but you have to factor direct sunlight and protect accordingly. If you consider that 3 faces of a building can get direct sunlight you are pretty much limited to the north facing parts of the building and ideally it is better to use a black sheath.

Was quite surprised black was better because it absorbs UV rays but I guess absorbing them is a better blocker?
It’s the fact that carbon black is a good barrier against uv and it is generaly used as a pigment in the cable manufacturing.
Other colours require expensive uv protection additives instead.
 