Is it (the stove, stands alone, no pipework apart from SS flue up through the roof) an Extraneous Conductive Part or not?
 
What I would really like to do is return to the subject of Emma Shaws' electrocution and what we can learn from it.

As I have said; in my day metal stud partitions had earth continuity without us even having to think about it (knockout boxes fixed to metal noggins etc. etc.) but installation methods have now changed, the use of plastic back boxes obviously breaks the continuity between the earthing system and the upstands.
It has become obvious from this example that plasterboard, once it gets wet is not the insulator we were all hoping it would be therefore in this example we can claim that it probably wasn't 'reasonable foreseeable' that there would be a problem, but that excuse should only be used once.
Now that we have experienced what can go wrong we need to act upon this knowledge and start connecting fly leads from sockets/switches/spurs that are mounted in metal stud partitioning to the partitioning upstands!

Are we in agreement that this is now the way forward? In my opinion it is the responsible thing to do.
 
and take a fly lead to the metal windows whilst we're at it.
 
Can it be gripped arch?
Will it extend the duration of a shock if it should become hazardous live?

Now I know whatever I say you'll disagree and start crowing and shouting your mouth off so I'm glad that the ultimate decision is that of the electrician responsible for the system, in this case you old son.
 
therefore we bond the worktop in order to automatically disconnect the supply and prevent it from becoming hazardous live but we do not need to bond the table.

Simply looking at fixed steel worktops in a kitchen and imagining what could happen if they came into contact with a damaged flex should put the fear of God into you, if you leave all that metal unbonded and someone gets hurt/killed you would deserve to go to prison!

David mate, a post like this only serves to demonstrate how little you know about equipotential bonding and yet you masquerade around as an electrician who has a deep and sound understanding of the subject. Hell, you even write books about it that are available to the general public!

My advise, stop what you are doing before someone gets hurt as a result of your writing, whether that be a post in this forum or from a page in one of your books. I can see from your posts that you are nothing but a charlatan that knows sod all about electrical work but joe public won't. You're a danger to yourself and others, please, I beg of you, just stop!

Finally, if you would like a few lessons on equipotential bonding and/or protective measures, these are subjects that I happen to be very knowledgable in. I don't know where you live but if you're anywhere in the South East I'd be more than happy to teach you the subjects in question correctly, I don't charge very much either as I enjoy the subject :) Who knows, after you've gained a proper understanding of the subjects you might be able to edit your books so that they are correct and are no longer a danger to people.
 
Come on Dave,
I don't want to rehash the tragic event that was resolved 5 months ago.
Answer my stove/radiator bonding question!
 
i'm beginning to doubt my sanity. who in their right mind would shove a vacuum cleaner in a stove? the hot ash would burn the paper bag.
 
How many more times are you going to go on about metal windows tele?
I've told you a number of times that I have suggested 'insulated handles' in order to save us having to bond the damn things.

Now the big problem and the reason that bonding them first became an issue was the condensation associated with single glazed 'crital' windows therefore double glazed modern windows are an issue that for me anyway is yet to be resolved.
Do you have problems with condensation with double glazed windows?
Perhaps you could try explaining the potential problems to your client and then ask them whether or not they want you to bond them, and then note their reply on your test sheet.
 
Skelton - the pot calling the kettle black old son, you know nothing useful obviously and are a danger to yourself and others undoubtedly.
Archy - this is a thread about Emma Shaw and whether or not you bond your stove is your decision I've not seen it.
Tele - you vacuum a stove or fire place in the summer when it cools down.
 
strange. that's the first time i've mentioned windows. not got a problem here. they're all plastic or wood. but wait. the handles are brass. just going to the wholesalers to buy 50 BS951's.
 
:banghead:

Dave,I think you know what I'm trying to do here!

I'm unsubscribing from these threads and off down the library to read your books. :-)
 
Skelton - the pot calling the kettle black old son, you know nothing useful obviously and are a danger to yourself and others undoubtedly.

Erm, ok, and that conclusion was reached how???

David 'old son' (not that I want to come across as a patronising w****r) why do you feel the need to spit in my face after I extend my hand to help?
 
if you will insist on extending your hand to feed the troll, what do you expect?
 
After many years of insults and attempted wind ups on the IET forum finally some people began to put forward their genuine thoughts and it soon came to light that their confusion over earthing was caused by them not recognising the difference between the role of 'equipotential bonding conductors' and 'supplementary equipotential bonding conductors'.
I wonder if the same is true of this forum.
 