I have two consumer units fed via henley blocks from the meter and 100amp fuse.

The original plastic cased CS from 2003 with 25mm tails. There are three slots available in this CS.

The second is a recently installed small metal cased unit feeding my heat pump and a small 2.4KW solar PV. This is fed from 16mm tails and also has three slots available.

I'm 'considering' buying an EV and thus having a 7.4 Kw charger fitted.

Can any potential issues be seen with the above?
 
its not "how many free slots in the CU" that is the issue, but how much power can be taken through the CU's..... depending on the loads at the moment and what can be safely added to.

It may be that a 3rd CU should be added, just for the EV.... which may also mean the addition of a surge protection device... if you dont have one already.
 
its not "how many free slots in the CU" that is the issue, but how much power can be taken through the CU's..... depending on the loads at the moment and what can be safely added to.

It may be that a 3rd CU should be added, just for the EV.... which may also mean the addition of a surge protection device... if you dont have one already.
There is no room for a third CU, not without a major upheaval. I'm not keen on one outside the house if it can be avoided. I have a surge protection device in the HP / Solar CU. The installer for the charger wants two slots to take the double pole RCD.

So looking at the current draw. The heat pump has a maximum current draw of 11.2 amps, the charger will be around 32 amps, and the Solar PV is 11 amps at most. The chances of the heat pump being on full whack during the winter with max sun and the car on a 8 hour charge would be unusual. If it were, all three on full chat would be around 54 amps through 16mm tails.

Not a lot of headroom if santa brought the sun, the temp was -10 decree's, and I was charging every day
 