Looking at using a fairford synergy soft start unit as below to start a 45kw motor, just wondering what it means by connected in line, I’m presuming they mean star but can see how the motor would run correctly being 400/690v rated?

https://inverterdrive.com/file/Fairford-Synergy-Quick-Start-Guide-V03

I’m thinking it needs to be in Delta to get 400v across the windings.

It’s also asking for 250a mccb protection via an inverse time delay mccb, or alternatively use fuses.
Struggling to find a inverse time delay mccb but it would be my preferred method.
 
On page 9 of the reference there is a note which explains how a synergy soft starter of a lower current rating than the motor can be used provided that the motor windings are wired Delta and the synergy is wired into them as shown in diagram so that it controls the current through each winding rather than the current to a pair of windings.

When wired in-line (or in series) with the motor the synergy must be rated to control the full line motor current.

If your supply is 400V, then the motor windings must be wired for this line voltage - so yes in delta.
 
Circuit breakers which include a thermal overload functionality to detect overcurrent are inverse time delay types. The manufacturer advises the use of a UL marked mccb - UL is an American scheme - but UK manufacturers can supply suitable mccbs. See:

MCCB-UL 489 Listed Molded Case Circuit Breakers - https://www.omega.co.uk/pptst/TD_TS.html

The manufacturer advises the use of both an MCCB and a semiconductor fuse see note #2 page 17/20 to provide enhanced protection against damage to the power electronic components inside the synergy. Suitable 250A semiconductor fuses aree suggested. See:

http://www.cooperindustries.com/con.../Resources/Catalogs/bus-ele-cat-10506-hsf.pdf

and

Bussmann | Page 513 | Kempston Controls - https://www.kempstoncontrols.co.uk/m/bussmann/page/513
 
Marconi
Thanks for the reply, so when it says line it means series as in two windings in series (star) however I can get away with using a smaller soft start if wired in delta. I need to clarify the the trip class so I’ll leave this until I find out.

Back to the circuit protection, I don’t have a sufficient supply (only 160Amps) to use 250A mccb, the motor was running off 100A bs88 fuses (started via star/delta starter) and it was fine, can’t understand why they call for such a high rating.
 
250A is way over required for a 45kw motor, I see no harm in going below this. I see problems if you exceed the 250A but not reducing it.
 
Re your #4 - When wired 'in-line' that is in series with supply cable to the motor, the motor windings must be configured for 400V if the source of supply is 3 phase 400V. I assume for the motor you are dealing with that meant wiring the windings in Delta, since the same windings could be wired in Star configuration and energised by a line voltage of 400 x 1.73 = 692V.
 
Last edited:
Here is the contact number for Fairford Electronics Ltd:

Contact Us | Fairford™ Soft Starters - https://www.fairford.com/contact/

for you to seek some clarfication.

The sizes of the fuses and mccbs they recommend are for short-circuit protection of the Synergy soft-starter and are the maximum size for each of these short circuit protection devices taking into account the prospective short-circuit current. So, as Westward10 said they can be smaller sizes but not higher. Before you phone see if you can find out the pssc for your supply.

The Synergy has electronic functionality to monitor motor currents and detect overload/overcurrent and then trip; see page 15 ''motor overload 'cold'trip curves''.
 
I agree FLC is only 77Amp I was planning on a 100a mccb starting current should be relatively low with the soft start.

I have emailed fairfords for further advice.

The motor will be wired in the delta configuration however this has brought up more issues as the soft start is remote from the motor, I need an appropriate 6 pole isolator.
 
Do you think it can be connected in delta and then 3 wires to the motor like you would connect a VFD?
 
Re #11: Yes, if you connect the motor ('it') in delta at the motor's terminals and then use the 'in-line' wiring method to connect it to the Synergy. You would then only require a 3 pole switch-disconnector.
 
You need to work out what is meant by the terminology of placing a soft start inline and in delta (more often called inside delta). The motor could be wired in either star or delta, for both configurations of the soft start. Providing it is a 6 lead motor.

This will probably help you understand:

Soft start circuit: how does it differ among soft starters? - http://www.soft-starter.co/soft_start_circuit.html

It also explains why you get away with using a smaller soft start whilst inside delta.

Your mentor/senior person that you are working with should know this.

Edit: semi conductor fuses require a lot lower Zs to operate and operate a lot faster than normal fuses. They are installed to prevent damage to the thyristor stack in the soft start, they are not designed for over current protection. This will be provided by the soft start or if not, you will have to provide it by other means.
 
Rob,

Thanks that has cleared the motor configuration up, the motor will be connected in the "inside delta" configuration however i will keep the soft star specification at 45Kw this will allow for frequent starting of the blower up to trip class 30, so it should increase reliability for the sake of very little extra cost.

Im still not 100% on the circuit protection though, it states a 250A Semiconductor fuse (class aR) is that in addition to a UL Listed inverse-time delay circuit breaker
 
No need to follow UL requirements as I presume this work is stopping within the UK?

UL have some funny workings, probably not worth me explaining as I don't think you do work in the US (correct me if I'm wrong an I'll explain) there's no need to have the circuit breaker and the semi conductor fuses.

Just ensure that the thermal protection you're utilising disconnects all of the phases to the motor. Via hardwired interlocks or position within the install.

Edit:

As stated before, the maximum protection you can use is 250A, personally I'd probably stick 125A fuses and have done, but you mentioned a high duty cycle, so you may actually require the larger fuses to deal with the heat cycling.
 
Last edited by a moderator:
Thanks Rob, The duty cycle isn't that high maybe 5 starts per hour, The Soft start has facility for PTC termistor input so i'll go with 125A fuses.
 
What type of 125A fuse? Why go up from 100A BS88 to 125A type? when the Synergy motor start is softer than previous star-delta? Has start-stop regime changed to something more onerous/frequent? Is cabling suitable?
 
What type of 125A fuse? Why go up from 100A BS88 to 125A type? when the Synergy motor start is softer than previous star-delta? Has start-stop regime changed to something more onerous/frequent? Is cabling suitable?

BS88 fuses can't react under a fault quick enough to protect the electronics inside the soft start.

Semi conductor fuses or type J can protect them, however due to them being able to react so fast, they also can suffer more from nuisance tripping if the circuit is under a high start duty.
 
Going to go with 3 x

Ferraz Shawmutt - 125A High Speed URD 22 x 58mm Semiconductor Fuse

621 CP URD 22.58 125 (A 220708)
 
No need to follow UL requirements as I presume this work is stopping within the UK?

UL have some funny workings, probably not worth me explaining as I don't think you do work in the US (correct me if I'm wrong an I'll explain) there's no need to have the circuit breaker and the semi conductor fuses.

I just copied and pasted from the datasheet, no I don’t do work in the US, in a previous life I used to do a fair bit of product design, most of which eventually went on to be sold in the US so it involved having our products UL approved, it was an absolute nightmare getting the stuff through!
 

Reply to Fairford synergy soft start unit in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi I have a question on soft starts. Why do soft starts have motor FLC delta /1.73. I’m confused as I understand star delta it is set at 58% of...
Replies
17
Views
3K
Hi all, Got a bit of a problem with a new generator when starting a 60hp motor. It's a 250kva generator with a 125A mounted plug, the plug is...
Replies
49
Views
6K
D
Hi there I am used to seeing dual voltage motors stating delta 400V Star 690V and my understanding of this is The line voltage in delta is the...
Replies
12
Views
2K
D
Hi I previously made a similar post howeverjust want to ensure ive grasped this, Found an explanation of star delta on awebsite although don’t...
Replies
14
Views
2K
M
Hi is anyone on here using the cable mate software? Ive just bought it, just waiting for my registration code to come through. It looks very...
Replies
5
Views
5K
E

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock