Guitarist
The core of the problem though, is that as you have already pointed out, electrical work needs testing. DIY'ers do not have test gear, or the training to use it.
An example of this is when the homeowner has diligently connected their shiney new metal light fittings, but wasn't able to carry out testing. On several occasions now, I have come across no earth connection between the fitting and the CU, due to DIY electrics carried out (often in the loft) resulting in cpc's being disconnected. Only an R1+R2 test (or a simple R2 test) will confirm this.
The DIY'er has done what they consider to be a good job, but has in fact left a dangerous situation. Of course, "it works dunnit" so nobody is any the wiser.
This is just a simple example, and there are loads more I could give.
An example of this is when the homeowner has diligently connected their shiney new metal light fittings, but wasn't able to carry out testing. On several occasions now, I have come across no earth connection between the fitting and the CU, due to DIY electrics carried out (often in the loft) resulting in cpc's being disconnected. Only an R1+R2 test (or a simple R2 test) will confirm this.