Fault protection on distribution cable

After some advice place. Been to look at a EV charging job today cable is already ran 16mm EV tuff flex fitted at 7/8meters high. clipped direct for a 50ish meter run my thoughts are to put a EV C/U one end with the car charger straight in to that with a 40 amp 30ma rcbo and spd in it. at the main ends in the shared supply cupboard I was thinking of putting a switched fused isolator. But this would only other overload protection. So what am asking is would the distribution cable also need the same levels of fault protection. Thank you in advance
 
Are you suggesting the fuse at the switch-fuse would only provide overcurrent protection and not fault protection?
 
Sorry my under standing is that it others short circuit protection and over current. But no earth fault protection. (I'm aware short circuit is fault protection my bad for how I've wrote it)

Are you suggesting the fuse at the switch-fuse would only provide overcurrent protection and not fault protection?
 
Your profile states you are a trainee is this still the case?
Do you understand the principles of automatic disconnection of supply (ADS)?
 
Your profile states you are a trainee is this still the case?
Do you understand the principles of automatic disconnection of supply (ADS)?
So not technically fully qualified as no NVQ but every thing else Including AM2. Served most my time on maintenance jobs. And yeah automatic disconnect. So in my head it's a distribution cable so sits in the 5 second margen if I'm correct. Tbh most evs I've done tend to be short runs with mains in the property so can usually just split tails fit board and crack on with the run. But cause this is a little different to my norm. Not sure if I'm getting into my own head an over thinking on it
 