A

assegayer

Okay guys this has been bugging me for a while..

What im thinking is that if you fit an FCU say on a cooker circuit to power a hob igniter (just an example) you would say put a 1amp fuse, how does this even work.

i mean wouldnt you still be getting like 40 amps from the oven going through the flex coming out of FCU therefore melting the flex because it cannot take the ampage? and then sometimes i hear different things from different people one person will say the fuse protects the actual load the next person will say no it protects the cable????!!

or does the FCU just simply take the amp it needs when it needs it?

i hope this is clear

thanks
 
the load (in this case, the igniter) determines the current drawn. if there's a fault, then excessive current will be drawn, thus causing the fuse to blow.
 
ohh okay, its just wouldnt the ampage from cooker circuit flow into the fcu aswell because the conductors are connected up with the cooker circuits ones aswell? also is this right? the fuse protects the cable and not the load right?
 
fuse protects cable against overload. any protection for a load will be incorporated within the load itself.
 
oh okay thats finally cleared that up in my head..also earlier you mentioned of if a fault where to occur..what kind of fault?
 
If you believe the current from a load will flow through a separate branch of a circuit because they are connected together, then think about what happens at the consumer unit; all the circuits are connected together so does the total current from any item flow though all parts of all circuits?
The house is connected to all the other houses and the industrial estate nearby, does the current from there flow through your lighting circuit?

This is the difference between series and parallel circuits.

In general all 230V equipment is usually connected in parallel so that they all see the same voltage (nominally 230V) however the current is split to each load individually.
 
i have actually never thought of it in that way i just dont understand why in college they cannot explain it like guys on a forum can :mad2:


just on last question i dont want to drag on or do your head in

why can a radial take 20 amps yet a ring can take 32 amps....surely the cable will burn out on the ring because its the same 2.5mm2 cable??? i know a ring has 2 legs so its more cable but shouldnt it be double then and be somthing like 40amps??? :whatchutalkingabout
 
That is a difficult question because even though there are two conductors in a ring and so effectively there is double the current carrying capacity, the current flow down each leg of the ring is not equal, a socket very close to the start of the ring will draw the majority of the current through the short leg of the ring this means the cable at that point could be overloaded if you were to protect the ring with a 50A breaker.
The idea is to ensure the current, even when unbalanced, does not exceed the part of the ring taking most current.
 
Last edited:
Really appreciate all you answers, thank you both of you, very good at explaining things :smile:
 
think about it like water in pipes. if you have a branch pipe with a partially closed tap at the end, then the water flow down that branch would be a lot less than the flow down the main pipe.
 
The ring main question is a lot more complex than you could imagine and is based on quantum physics, to try simplify it a simple statement is true:-

Current will flow down the path of least resistance.

Now excluding super conductors for the minute, every conductor generates heat when current flows, this heat creates resistance now where you have one route this has little effect as to the path of current but where you have a ring with 2 paths this generated resistance effects the current flow as it see saws the current flow between the two directions - as one path resistance increases above the other the current starts to rise in the lower resistive leg till it exceeds the value of the first leg and this repeats billions of times a second and your current on each leg is decided by the resistive balance... because in the concept of things that ringmains are relatively small, clamping each leg will show a roughly equal load share no matter how close to the CU a socket may be down one leg.

Influences of current balance is really anything else that would create resistance so other loads, poor terminations, cable length to some extent are all examples but it would be wrong to say or think current flows down the shortest path... it follows the path of least resistance thus a ring is self balancing and shares current flow down both legs regardless of socket position.
 

OFFICIAL SPONSORS

Back
Top