Buzz-light-bulb

Can someone explain to me why am getting 230v across neutral and cpc on lighting circuit, now I know it's because there's a missing neutral but I just can't understand the technical side to it, If someone can nicely explain it would be much appreciated
 
if the neutral from where you are testing to the CU is broken, then you will have 230V on the L side of the load. with the load switched on, there's no volt drop as there is no current flow. hence 230V on the neutral side of the load.
 
If you switch all the lights off or take the lamps out it will or at least ​should disappear
 
What Tel said up there ^^^^. Draw yourself a wiring diagram and it may make it clearer how the current is flowing/not flowing, and why the voltage remains present. Daz
 
if the neutral from where you are testing to the CU is broken, then you will have 230V on the L side of the load. with the load switched on, there's no volt drop as there is no current flow. hence 230V on the neutral side of the load.

Thanks tel
 
If it int as per Tel or Monkey, then check the polarity, is it a neutral connected wrong? I think they will be nearer the mark than me, but it is worth a mention, cos if it is it will be as you say.

Cheers……………Howard
 