Hey guys just a quick question I have got a job on supplying a shed from a first floor CU. would a feed from the board in flat 6mm to an outside junction box then 6 mm SWA from the junction box to the sub board in the shed. Although the earths connected in the JB would be of different sizes I.e 6mm and 2.5mm is this ok or is there a different method I could do this ?? Any info much appreciated
 
depends on the earthing system and whether there's any extraneous in the shed. if it's TNC-S and you have extraneous in shed then you need a 10mm earth. if not, then you can run a separate 6mm gn/y along with the T/E if it needs it.
 
No extraneous in shed so all I need is a metre of 6mm earth and connect in junction box to board and disconnect the earth from T&E???
 
can do. depends on the csa you need after applying the adiabatic equation. and don't forget the earth the SWA armour, even if not using it as cpc.
 
No extraneous in shed so all I need is a metre of 6mm earth and connect in junction box to board and disconnect the earth from T&E???
whats the demand in that shed....
whats the length of run
any lighting in there...
whats the installation method
 
Yeah got that glennspark :) so rather than goin inside the house with SWA I have drilled out with 6 mm T&E and connect up in JB but I need to run some 6mm earth to JB as the earth in the T&E isn't sufficient am I right ??
 
CU on the first floor, if this is a flat, you need to get the owner to check their agreement regarding attaching the cable to another part of the property - most leasehold agreements do not allow this.

I'm guessing the shed is for growing weed!
 
No it's the 1st floor of a house and the heat lamps are for his kennels when his dogs have pups
 