Had a joiner in doing some work and he managed to screw into the existing main earth which is a 25mm cable in a tt system. I tested it and I'm getting a Ze of 0.26 and PEFC of 9A. Should I replace the cable?
 
Last edited by a moderator:
Well the only way I know it's damaged is that I'm getting continuity between a screw and the main earth. To what extent it's damaged I don't know.
 
But say I didn't know about it Dave? It wouldn't be found once testing is carried out would it?
I agree with you that it should be replaced and I will. I was going to go a step further and put new rods in.
 
But say I didn't know about it Dave? It wouldn't be found once testing is carried out would it?
I agree with you that it should be replaced and I will. I was going to go a step further and put new rods in.

If you didn't know about it then you wouldn't even be thinking about what would happen if you didn't know about it. But you'll need a philosophy forum for that!

Replaced maybe, or repaired, depends on the exact situation and what will be least disruptive.
 
Surely it would be the same on any job - if a cable is known to be damaged then you fix it? Daz
 
If it's damaged it needs fixing but the screw isn't the cause of the 26Ω. I don't think you can sever a 25mm² with any woodscrew known to man, but to have any impact on a real world Ra there would have to be a sliver of copper left smaller than a human hair.
 

Reply to Flippin!!! joiners! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
739
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock