dawg25g

Have anyone had any problems with self regulating heat cable. I installed frost protection cable on to a water pipe that was feeding water troughs in a slatted cow shed. The customer went nuts when the water pipe burst. The tee joint that i had installed had failed and disintegrated, must have been arcing across the conductors. I dont know how this happened, i was sure that the joints were done correctly using bn thermal tee joint heat shrink kits. The cable is in a really ****ty damp enviroment, my thought is that dampness is the cause. I have now redone the joints and used compression tape to seal them. The cable manufacture say they have not had any failures so im thinking its my handiwork to blame.
 
Sounds like there was a problem with the joint. I've used heat shrink with a little silicone sealant inside before it's shrunk, then a quick wrap of non-drip tape around the joint and around the whole pipe if necessary.
 
Markie - was going to say exactly the same thing. My outlaws have an enormous dairy farm down here and last winter spent days on end defrosting pipes - but they wont have trace heating installed as the cows just chew at it.

Trivia: ONE dairy cow drinks in excess of 8 gallons of water a day. That's why frozen pipes are such a big deal.
 