Discuss GT Excitation system in the Industrial Electricians' Talk area at ElectriciansForums.net
S
speedtronic
With reference to GE frame9E GT Excitation system(rotaduct/rotating diodes), Why DC excitation voltage is not directly applied to rotor?
I mean that DC excitation voltage coming from excitation panel is first applied to exciter stator & consequently on exciter rotor, we get AC voltage which is then again converted to DC voltage through rotating diodes which give this DC voltage to generator rotor? What if we apply DC voltage to generator rotor directly which is coming from excitation panel?
well done, you just uninvented the brushless generator:p
What you have is a two stage brushless (a three stage is where the initial excitation comes from a permanaent magent on the rotor)
The power is applied to the exciter stator, which then induces ointo to the rotating pick up field, you are then rectifying, and applying the DC to the rotor field, which is then inducing into the three phase stator output windings.
Yoiu will find that the AVR is also in the excitation panel, and this senses the genny output, adjusting the excitation field accordingly.
This is how we have a brushless system - there is no connection between rotor and stator.
If you were to apply power to the rotor directly, then you would have to be using sliprings and brushes- with the obvious maintenance penalty that this will incur;)
Reply to GT Excitation system in the Industrial Electricians' Talk area at ElectriciansForums.net
I have been asked/invited to "post more", lol, so let me make another post right away. I thought of sth worthy to post, of interest to many, I...
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
We have 10 energy meter in that 4x of them are giving the negative reading. The events shown are two 1is Negative Power Element 2 Warnings & 2...
Hi again. Following my recent zero-Riso issue (unresolved) and also because my system has, in any case, been prone for a good while to the odd...
Electrical2Go - Green2go Launches for All Your Solar, EV Charging and Renewable Needs Green2Go - for All Your Solar, EV Charging and Renewable...