DurhamSparky

Well lads if the regs taught us any thing its to check your earthing and bonding!!!

for the last 3 days Site Supervisor and 4 Techs have been trying to fault find a N-E fault on a ABB monitoring unit. apparently the U was jumping about around the phases and the had 50 v N-E....

i happened to overhear this conversation about the supervisor going on about the monitoring unit and saying well we will have to get ABB in to fix it.. blah blah

any way its my first shift back from 4 off and i said do you want me to have a look...! i got the usual "if you want to" from the site manager but we think its a manufacturing fault!



long story short, new power distribution unit and cabinets, 3P+N + Clean Earth all connected...

main Earth Bar with all Supp bonding running back to it was just floating with out a path to earth...! ran a temp 6mm bond to the next unit that had been earthed by the original installation sparks.

Oh Look the N-E fault has cleared and the 50v has "vanished"

supervisor and management told me to keep my mouth shut!
 