Ok guys, hoping you can tell me what I've missed......
Hager 10 way board, all 30ma type B rcbos. I installed the board about 13 months ago. Customer advises that ring final (covers both ground and first floor, excluding the kitchen) is tripping intermittently over the past four weeks, but thinks it's happened as she has been switching off a switched fused spur serving under unit flories in the kitchen. But, the kitchen is on it's own hybrid circuit (ring final off a cooker radial).
I have been unable to reproduce the fault.
TNCS supply, good Ze; both circuits IR fine, no linked neutrals; connections in the board are all in the correct rcbos and tight; switched fused spur (no neon) serving under unit lights checked - all connections good, switch feels fine; ramp tested rcbos - 24ma on both. Tested four Class 1 lamps on the ground/first floor RFC - all fine (one did have a Phillips cfl which I changed for a standard lamp, just in case). Nothing else of particular note on this RFC.
I'm struggling to think of anything else. The SFS in the kitchen could be a red herring, but the customer is fairly on the ball so I don't want to rule it out completely.
So, am I missing something (other than a crystal ball!)?
Regards.
Hager 10 way board, all 30ma type B rcbos. I installed the board about 13 months ago. Customer advises that ring final (covers both ground and first floor, excluding the kitchen) is tripping intermittently over the past four weeks, but thinks it's happened as she has been switching off a switched fused spur serving under unit flories in the kitchen. But, the kitchen is on it's own hybrid circuit (ring final off a cooker radial).
I have been unable to reproduce the fault.
TNCS supply, good Ze; both circuits IR fine, no linked neutrals; connections in the board are all in the correct rcbos and tight; switched fused spur (no neon) serving under unit lights checked - all connections good, switch feels fine; ramp tested rcbos - 24ma on both. Tested four Class 1 lamps on the ground/first floor RFC - all fine (one did have a Phillips cfl which I changed for a standard lamp, just in case). Nothing else of particular note on this RFC.
I'm struggling to think of anything else. The SFS in the kitchen could be a red herring, but the customer is fairly on the ball so I don't want to rule it out completely.
So, am I missing something (other than a crystal ball!)?
Regards.