Builder has run 2.5mm t&e feed from 16a radial to integrated rcd outdoor socket. New board put in by builder (part p registered - i'll say nowt)
I am asked to extend the radial out to couple of sockets and a spur feeding a pendant.
All wired in fine and i start getting odd readings when trying to do Zs. 230 between everything except live and neutral at every point aling the circuit from first point to last. I checked polarity in all points and it also meggered out fine.
I took the rcd socket out of action (term blocks connected behind faceplate!!) which remedied it. But then in the first socket got a zs of 0.48 ohms but second socket about three metres away (all connections definitely sound) zs was 6.3 ohms. Ok it's below 1667 so 'within regs' haha but that seems well odd right?
Think this is 2 seperate faults. Possibly old rcd socket had water in it but wouldnt this short rather than changing polarity mysteriously?!?!
And dodgy socket giving h
I am asked to extend the radial out to couple of sockets and a spur feeding a pendant.
All wired in fine and i start getting odd readings when trying to do Zs. 230 between everything except live and neutral at every point aling the circuit from first point to last. I checked polarity in all points and it also meggered out fine.
I took the rcd socket out of action (term blocks connected behind faceplate!!) which remedied it. But then in the first socket got a zs of 0.48 ohms but second socket about three metres away (all connections definitely sound) zs was 6.3 ohms. Ok it's below 1667 so 'within regs' haha but that seems well odd right?
Think this is 2 seperate faults. Possibly old rcd socket had water in it but wouldnt this short rather than changing polarity mysteriously?!?!
And dodgy socket giving h