Eddiesparks

Builder has run 2.5mm t&e feed from 16a radial to integrated rcd outdoor socket. New board put in by builder (part p registered - i'll say nowt)

I am asked to extend the radial out to couple of sockets and a spur feeding a pendant.

All wired in fine and i start getting odd readings when trying to do Zs. 230 between everything except live and neutral at every point aling the circuit from first point to last. I checked polarity in all points and it also meggered out fine.

I took the rcd socket out of action (term blocks connected behind faceplate!!) which remedied it. But then in the first socket got a zs of 0.48 ohms but second socket about three metres away (all connections definitely sound) zs was 6.3 ohms. Ok it's below 1667 so 'within regs' haha but that seems well odd right?

Think this is 2 seperate faults. Possibly old rcd socket had water in it but wouldnt this short rather than changing polarity mysteriously?!?!

And dodgy socket giving h
 
If you have 230 between everything except L and N you have a lost neutral connection at some point

as for high zs reading are you measuring from a plug in lead or probes at the actual terminal points on the socket

cheap sockets can give you bad readings when you plug a meter into the socket

Probably sounds like you will find a choc block with tape wrapped around it in a wall or under a floor some where, where the builder left the cable too short and had to do a builders join, probably where your lost neutral and bad earth readings coming from
 
Ps thats high zs sorted. Plug in probes and cheap socket. Seen it before but never this bad. Thanks mate
 
If it is a lost neutral why is there 230 between earth and neutral?

Thanks

Think about volt drops across resistors in series - If the neutral was connected then 'all' voltage will be dropped across the load, if disconnected you have the load and 'fresh air' in series - which is the higher resistance?
 
But in that case you'd have around 120V rather than 230V normally?

No because the load resistance will be very low compared to the extremely high resistance of the 'fresh air' - as I said consider voltages in series resistor circuits.
 
just consider the load with a disconnected neutral. there's no current flow, so no volt drop so what ever voltage is on L side of load will also be on the N side. QED.
 
just consider the load with a disconnected neutral. there's no current flow, so no volt drop so what ever voltage is on L side of load will also be on the N side. QED.


Quite but you can never actually test this 'no current' voltage because as soon as you put your voltmeter on it current will flow :)
 
true, but a very small current. all depends on the meter's input impedance. very high with digi meters.
 
This is the hazard with borrowed neutrals -

You disconnect and remove the upstairs lighting feed from the DB and turn everything back on -
You are certain that the t&e you have removed is absolutely and definitely dead -
Someone switches on the landing light and your disconnected cable neutral becomes absolutely and definitely LIVE!

Result - small amount of volts dropped across landing lamp, huge amount of volts dropped across YOU!

:)
 
solution .. isolate both circuits. then see if client will pay for remedial work.
 
i meant isolate both while working on it. not leave it isolated. can't do smiley as the options gone.
 