I think i get it! Like when u disconnect neutral from board with load connected and mcb closed it becomes live. You only make that absent minded mistake once !
 
I think i get it! Like when u disconnect neutral from board with load connected and mcb closed it becomes live. You only make that absent minded mistake once !

like a bet?
 
Have i got it then? So there is no voltage between l and n because both are live (and of course the same phase!) because load connected.

In the same way a switched live (switch open) with lamp in is by default a neutral.

Is that it then? Thanks for patience i kind of knew it but needed a bit of help getting there.

I think some confusion arose from when u have missing earth and you get odd (sort of half mains) voltages between earth and live.
 
about right. if the earth ( cpc) is not actually connected to earth, then it is "floating" and can have a potential on it. either from a fault , or induced by being in close proximity to cables with voltage on them.
 
Sometimes had high readings when customer bought sockets and found it to be the springs inside. Assuming you just plugged in, it's fixed the issue when you simply jiggle the plug in the socket. You will especially notice this when your reading is jumping up and down, same thing cures it more often than not. Let plumbers be plumbers and builders be builders I say!!
 