? Pretty sure it does. What do you make it?:)
I was only kidding-----but it actually makes 230.94, that makes the current 15.396 amps not 15.33, not that it really matters, you have taught me something today mate, thanks, seriously good job fella.
 
I was only kidding-----but it actually makes 230.94, that makes the current 15.396 amps not 15.33, not that it really matters, you have taught me something today mate, thanks, seriously good job fella.


You are correct lol. You had me worried for a second. :hand: :smile:
 
I find it highly annoying that the formulae for calculating Line & Phase current in Delta requires knowing either the Line OR Phase current.

You have the voltage. You have the Ohms. V/R = I. Both phase voltage and line voltage is the same in delta. But the line current is route 3 x the phase current.

So to get the phase current it is, 400volts / 15 ohms = 26.66666667Amps . Then 26.66666667 x 1.732 = 46.18666667Amps Line current.
 
A handy rule of thumb also is that if you connect the same set of impedances in star and delta then the line currents will be three times higher in delta. This is because in delta the voltage across each impedance in root-3 times that in star, then the line current is root-3 times the phase current, multiply these and you get a factor of 3.
 
You have the voltage. You have the Ohms. V/R = I. Both phase voltage and line voltage is the same in delta. But the line current is route 3 x the phase current.

So to get the phase current it is, 400volts / 15 ohms = 26.66666667Amps . Then 26.66666667 x 1.732 = 46.18666667Amps Line current.


Thank you so much for clarifying this for me! I was focussing on IP = IL/1.732 too much, I was trying to use this to calculate current, when really it only shows the relationship IP&IL have in delta. Instead I should have simply been using ohm's law - IP = V/R, or IL = V/R*1.732.


However, I did notice that your answer for IL in delta was 46.1A, it is actually 46.2A. I don't know if this would matter in an exam.

There is only one more thing I'm unsure about, why 15 ohms? Don't they need to be added together?

It's Unit 302 (C&G 2365 L3)
 