Can somebody help me to work this out please? New to site not sure if I posted this question correct the first time.

A raidial socket outlet circuit is suplied by 2.5mm cable and is 20M long. Given the Ze of the installation is 0.43Ω and that the resistivty of the cable is 7.41Ω/m at 20c, what is the calculated ZS?
 
Zs=Ze + (R1+R2) x 1.2

R1+R2 can be calculated using resistance values per meter for a said csa
 
You will also require the resistivety of the CPC.

Zs = Ze + R1 + R2


Ps You do not multiply the result by 1.2.
 
by calculation how do i work out the R1 +R2?
I take it that the 1.2 is the denominate for 20oc
 
Can somebody help me to work this out please? New to site not sure if I posted this question correct the first time.

A raidial socket outlet circuit is suplied by 2.5mm cable and is 20M long. Given the Ze of the installation is 0.43Ω and that the resistivty of the cable is 7.41Ω/m at 20c, what is the calculated ZS?
Ive never calculated one, I always measure, thats said look at Geoffsd s post
 
0.7264.

well, he asked for the answer, not how to do it.
 
Can somebody help me to work this out please? New to site not sure if I posted this question correct the first time.

A raidial socket outlet circuit is suplied by 2.5mm cable and is 20M long. Given the Ze of the installation is 0.43Ω and that the resistivty of the cable is 7.41Ω/m at 20c, what is the calculated ZS?

It's milliohms/metre not ohms.
 
You will also require the resistivety of the CPC.

Zs = Ze + R1 + R2


Ps You do not multiply the result by 1.2.

oh but Im sure you doooooo use the correction factor to take into acount max operating temp of cable, and compare the value to BS7671.
So Zs = Ze + (R1+R2) x L x Cr
 
@ OP. multily the mOhms/m by the length of R1+R2, then add to Ze. show us your workings and we tell you if you is right or not.
 
oh but Im sure you doooooo use the correction factor to take into acount max operating temp of cable, and compare the value to BS7671.
So Zs = Ze + (R1+R2) x L x Cr

Several things:

OP did not ask for 70°. I think it's just an exercise so his answer would be wrong.
The way you have written it, you would also be multiplying the Ze.
OSG gives the values already corrected to 80% of 7671 (multiply by 0.8) so it's rarely done your way.
The Zs would not actually be at that figure when tested so your results would not match - so it's better to reduce the maximum allowed.
Splitting hairs now - it's multiply by 1.25 (divide by 0.8).
 
Hi Geoff,
yes your right i've made a mess of that formula it should be Zs = Ze x [(R1+R2) x L x Cr] and I did think perhaps thats going to give him an incorrect answer for C&G, but...the calculation is rarely done??
Surely its a design calculation, not one that would predominantly be used instead of testing, but it could, and lets face it even a calibrated MFT is not very accurate, get a group of testers all calibrated and they will give "almost" wildly different readings.
But get ya point :)
 
I think it would be safe so assume that the CPC is also 2.5mm as it is not stated in the question or said otherwise.
 
I would say that "cable" means something different to "conductor", but in the ops question it seems that they are using the term "cable" when they should be saying "conductor"
 