Thanks for the responseYour PFC should be the highest value between line/earth or neutral/earth. With TT it is always going to be the latter due to the high impedance between line/earth.
You are clearly using the line/earth impedance for your PFC and simple ohms law would give you around 1A (230÷200).
Is that line/neutral?Thanks for the response
Does that mean l can record PSC (2.6kva ) on my. report
Yea PSC (L-N) readingIs that line/neutral?
A ....1 Amp fault current would be considered very low and likely not a problem for a TT system, as these systems rely on RCDs (Residual Current Devices) for fault protection, which are sensitive to much lower fault currents. Each DB has an incoming 61008 Rcd and Extra main old Rcd protectionThe NICEIC EIC/certificates asks for 'Prospective fault current' Pfc not Psc although some certificates (Napit etc) may require Psc?
Entering Psc and not Pfc may lead to misinterpretation of the supply characteristics and a RCD may be omitted when in fact it will be required!
View attachment 122600
yes Pfc!rely on RCDs (Residual Current Devices) for fault protection, which are sensitive to much lower fault currents.