Hi please l did a testing on a TT system

Am having a reading of 200 ohms and my pfc is 1 amp @ loop high reading

With same 200 ohm
Pfc 1amp
Psc 2.67kva at a low reading
But am abit confused about the 1 amp pfc if its right
Its a new calibrated meter and its working perfectly
 
Your PFC should be the highest value between line/earth or neutral/earth. With TT it is always going to be the latter due to the high impedance between line/earth.
You are clearly using the line/earth impedance for your PFC and simple ohms law would give you around 1A (230÷200).
 
  • Like
Reactions: tochweens
Your PFC should be the highest value between line/earth or neutral/earth. With TT it is always going to be the latter due to the high impedance between line/earth.
You are clearly using the line/earth impedance for your PFC and simple ohms law would give you around 1A (230÷200).
Thanks for the response
That mean l can record PSC (2.6kva ) on my. report since
 
Last edited:
The NICEIC EIC/certificates asks for 'Prospective fault current' Pfc not Psc although some certificates (Napit etc) may require Psc?

Entering Psc and not Pfc may lead to misinterpretation of the supply characteristics and a RCD may be omitted when in fact it will be required!


1752429413845.png
 
The NICEIC EIC/certificates asks for 'Prospective fault current' Pfc not Psc although some certificates (Napit etc) may require Psc?

Entering Psc and not Pfc may lead to misinterpretation of the supply characteristics and a RCD may be omitted when in fact it will be required!


View attachment 122600
A ....1 Amp fault current would be considered very low and likely not a problem for a TT system, as these systems rely on RCDs (Residual Current Devices) for fault protection, which are sensitive to much lower fault currents. Each DB has an incoming 61008 Rcd and Extra main old Rcd protection
 
rely on RCDs (Residual Current Devices) for fault protection, which are sensitive to much lower fault currents.
yes Pfc!

BS61008 RCD's will not provide overload/short circuit protection - the Psc value!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
---
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Mac energy construction

Thread Information

Title
Hi
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
tochweens,
Last reply from
DefyG,
Replies
7
Views
157

Advert