extraneous

  1. J

    Domestic Bonding Extraneous Conductive Parts

    hi. Question re bonding a metal where cold comes in as metal pipe ground into house. So cold will be bonded where service comes in. Read article in wiring matters 2019 about changes for part 18. Example given of faulty kettle where fault to earth exists at kettle, some one touches kettle...
  2. N

    Extraneous Parts Earth sizing

    Customer wants to take power from an existing garage (with board) to supply a greenhouse, to be fitted with ip rated switchgear. The greenhouse is made of aluminium. Since this is an extraneous conductive part am i right in thinking that the aluminium frame would require a 10mm bond at least...
  3. S

    Extraneous conductive parts

    Morning, so just finishing off the install to a shepard hut which is located in a field. The construction is steel chassis, plyboard floor, timber stud clad with corrugated sheets. The corrugated iron sheets which clad the unit are plastic coated and there is no continuity between each sheet...
  4. kingeri

    Extraneous conductive part as bonding conductor

    Been nosying about at my brother's new house this week and fixing a few bits and bobs. The electrical installation mainly dates back to the early 80's at a guess and apart from a few broken accessories and a lack of RCD protection (now fixed) it has all checked out okay. PME earthing. Today...
  5. L

    Supplementary bonding

    Hello all, Perhaps a few of you could help my understanding of the following query. The situation I am about to describe is purely hypothetical to help my understanding of the issue. Let's assume within a domestic bathroom, I have a combination of exposed conductive parts and suspect...
  6. happyhippydad

    Main bonding made to separate earth rod?

    Evening all.. I have just been to a clients house to quote for some work and when checking the Main bonding I noticed that it just had a 10mm attached to the gas pipe and then straight into a separate earth rod, it was the same for the water (had it's own earth rod). I realise that this would...
  7. C

    Sup bonding

    just carried out and EICR on a grubby flat. One defect was lack of bonding in the bathroom without RCD protection. I don't want to change the DB to RCD everything. everything is wired in conduit, would I be correct in saying all I need to do is link a 4mm bond from the conduit to all the...
  8. H

    Steel Conduit

    Hi Just got a quick question. I install CCTV systems and want to start using steel conduit instead of PVC. Do I need to ground the conduit if it will only have CAT6 network cable inside. Thanks
  9. E

    Bonding of drain cover in tanked basement

    Doing some work on a building with a tanked basement. In one corner there is a drain cover that is an extraneous conductive part so I need to attach a bonding conductor. I was thinking of something I could bolt on to the rim (about 5cm wide) that wouldn't interfere with taking the cover off...
  10. Michaelwgroves

    Extraneous Conductive-part

    I've had my work assessed which has raised a question about Extraneous-conductive-part. I just want to be sure I fully understand this. BS7671 Part 2 defines it as; A conductive part liable to introduce a potential, generally Earthed potential, and not forming part of the electrical...
  11. A

    Outdoor Building Power

    It's been a while since doing any form of installation so I thought I may ask here for clarification especially with new regs...... Detached shed/building approx. 50m from house CU. Need to run 13A sockets and lights in it. TN-CS/TNS supply Is it best to... A) Take from MCB, then SWA down to...
  12. A

    Confirmation on testing procedure

    Hi guys another q I would like to clear up, when testing to confirm a pipe is extraneous in an existing install I use the equation 230/0.01 =23000ohms - 1000ohms= 22000ohms. when carrying out the test I test from the earth block to the pipe in question. just looking to confirm as I have just...
  13. yellowvanman

    EICR remedial

    Just done an EICR on an outbuilding that is habitable (kitchen/wetroom etc). Supply is taken from henly block in the meter cupboard, via 2 core SWA to building. At building SWA is glanded into a metal box but the box (earth) is not connected to the plastic consumer unit which sits right next...
  14. S

    Garage Metalwork

    I'm in the middle of putting some lighting and socket outlets in my garage, nothing fancy just a few of each as you'd expect. I've run it in SWA ,which will be buried eventually, from the existing CU in the house on it's own circuit. Earthing arrangement is TT which reads 14.67 ohms, not bad I...
  15. H

    EICR Code

    Would a C3 be adequate for a main protective bonding conductor connection to water not readily accessible? Connection is present (along with tag) but is under floor boards. Took me ages to trace it back. Also I can not verify the location of the gas bonding connection. What code?
  16. S

    Extraneous conductive parts in outbuildings

    Hi, i am after a bit of advice. I went to a property which had 3 outbuilding, all were separate from the main building, one garage, one shed, & a workshop. Circuits all supplied from main building. Earthing system is TT. In all of the 3 outbuilding there is a separate water supply with...
  17. S

    Earth Bonding garage framework required?

    Should the framework for my garage door be bonded? It is just controlled manually, it's non-electric. The framework is just bolted to the blockwork? Pictures below.
  18. E

    Quick Definition Help needed (No ref books with me right now)

    Would anyone be so kind as to reply to this post with the BS7671 wording of the definitions “Exposed Conductive Part” and "Extraneous Conductive Part". At work right now (without ref books) and trying to remember if the definition of “Exposed Conductive Part” is restricted to part of an...
  19. L

    Supplementary bonding required with RCD's?

    Much discussed issue this one. Appreciate any comments. I let a small one bed flat out. Electric only ie no gas. Year back I had a new CU put in with all circuits on RCD's (RCBO for lighting). Accompanied by an EICR. Registered ECA sparks did the work. The EICR documents that the mains...
  20. B

    Pir

    I have just changed some old 600 x 600 units over to spots with LED GU10's in some toilets and the spots flick on and off when they should be off. the switches are old PIR type with a battery in them. i have put a temp switch on one and it works fine but the client wants to keep old stuff. Help!
Electrical Insurance
ElectriciansForums.net (formerly known as ElectriciansForums.co.uk) was setup in April 2006 to provide free electrical advice to both professional and DIY electricians. Whether seeking advice for auto electrics, trying to find electrical installation condition reports (EICR) form downloads, or whether you're here just to talk to other electricians; we've been a first-choice website for tens of thousands of sparkies for well over a decade.