Hi all.
Looking for opinions on here.
I’ve identified during an eicr that a dry rise pipe used for firefighters in the building is in fact an extraneous conductive part and that it is not bonded back to the MET.
However what I’m questioning is it’s accessability to be touched in the event of a fault.
Pipework is installed in boxing with a key for an access panel for the riser water inlet to be used for the firefighters.
Only person with access is the building manager.
What’s people’s opinions does it require protective bonding or is it deemed not accessible to touch and that’s the end of the matter?
It’s worth pointing out bs 7671 doesn’t mention the fact it needs to be accessible however it’s common sense that says it needs to be if your going to be in contact during a fault between say an exposed conductive part and said pipework.
Thanks

To add the dry riser pipe comes up from the floor in metal and is separate from the cold water pipe entering the building in plastic.
A completely different service it seems.
 
Last edited:
How exactly have you determined this pipework to be extraneous?
Testing from the MET or rather the source of earthing to said pipe.
Main earthing conductor disconnected from source earth
IR set to 500v reading of 0.00 Mohms
Also no continuity between said pipework and a known earth source
 
Surely if someone can get to it then it is accessible?
The likelihood of someone coming into contact with the pipework during fault conditions is minimal to say the least but yes if the access panel is opened by key if say during an inspection or servicing of the pipework then it can be touched, perhaps this is my answer.
 
Testing from the MET or rather the source of earthing to said pipe.
Main earthing conductor disconnected from source earth
IR set to 500v reading of 0.00 Mohms
Also no continuity between said pipework and a known earth source
This is a block of flats or a tall multi user building I take it?
 
The Last Electrician probably didn't look tooo hard, but I think it should be bonded as that door could be left open.
 
might be worthwhile finding out why it's extraneous. bit of a grey area without some further info.
 
Doesn’t the fact that there is zero IR between the MET and the riser mean that the riser is reliably connected to the MET?
Thought the maximum resistance allowed between bonded parts and the MET was 0.05 Ohms?
 
Doesn’t the fact that there is zero IR between the MET and the riser mean that the riser is reliably connected to the MET?
Thought the maximum resistance allowed between bonded parts and the MET was 0.05 Ohms?

Are you getting mixed up between main and supplementary bonding?
 
Last edited:
Doesn’t the fact that there is zero IR between the MET and the riser mean that the riser is reliably connected to the MET?
Thought the maximum resistance allowed between bonded parts and the MET was 0.05 Ohms?
That is for main Equipotential bonding the OP is on about extraneous two different Animals, please see the vids I have posted.
 
Not sure what the videos are telling you, but if it’s that MEB is not intended to to equalise any possible differences in potential between extraneous-conductive parts then they are mis-informing you.
 
Doesn’t the fact that there is zero IR between the MET and the riser mean that the riser is reliably connected to the MET?
Thought the maximum resistance allowed between bonded parts and the MET was 0.05 Ohms?
No it means there’s little to no resistance between them or little to no resistance between the source of earthing and the metallic pipe which is introducing an earth potential.
If it was higher than say 23Kohms then I’d consider the pipework as not being extraneous.
There’s no such maximum resistance between bonded parts. 0.05 ohms is a value from GN3 which determines that testing between any two points such as metallic pipes can be considered reliably earthed/bonded
 
Not sure what the videos are telling you, but if it’s that MEB is not intended to to equalise any possible differences in potential between extraneous-conductive parts then they are mis-informing you.
Why is that Spin?
 
No it means there’s little to no resistance between them or little to no resistance between the source of earthing and the metallic pipe which is introducing an earth potential.
If it was higher than say 23Kohms then I’d consider the pipework as not being extraneous.
There’s no such maximum resistance between bonded parts. 0.05 ohms is a value from GN3 which determines that testing between any two points such as metallic pipes can be considered reliably earthed/bonded
Have you not just said the same as me, but in a more convoluted manner?
 
Extraneous conductive parts are considered as water, Gas, Oil, fire fighting pipework in high rise blocks, or large buildings, lightning conductors, structural steelework etc, ie they do not form part of an electrical installation
Seriously?
Are you telling me you are unaware of the purpose of Main Equipotential or Protective Bonding conductors?
 
Have you not just said the same as me, but in a more convoluted manner?
No not really.
It indicates that the metallic pipe is in contact with earth but as I’ve said, it’s not connected to the MET and has no continuity to it when using a wander lead to test it from the MET to the pipework.
The test I’ve done says to me it’s extraneous as it has a very low resistance to earth.
If it was connected to the MET then I’d have continuity.
Also the IR test I did was with the earthing conductor disconnected from the source of earthing and the test made between metallic pipe and the DNO source earth.
TN-S in this case on the side of the 3 phase Lucy unit with the earthing bolt.
 
No I just wanted you to explain your statement, it seems we are getting mixed up here Spin, of course I know the reason, it was just I thought your statement was a bit far reaching. And why you feel the vids are misinforming people that's all.
 
Last edited:

Reply to Extraneous conductive parts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

During an EICR I have come across a metal tap and copper pipes supplied by a blue plastic pipe. This measures 0.022 MegOhms, this is directly...
Replies
24
Views
3K
During an EICR I have found an isolator with no cpc present bolted to a large metal post and all the motorized metal car park gate, the fact that...
Replies
22
Views
3K
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K
I have just put in a sub distribution board in the middle of a field for a new supply for some poly tunnels (soil heating mats and lighting). I...
Replies
41
Views
4K
Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
Replies
8
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock