cliffed

-
Arms
Supporter
Reaction score
645
metallic portacabin used for offices,Swa is on a steel caternary,enters office to Rcd DB.
No separation of swa earth Tncs @ cabin.
I want to Tt it,what’s your thinking of caternary wire,it comes from building to cabin.
Will this still import Tncs,& will it also need isolation from cabin,where it’s fixed,obviously to the steel cabin.
 
Despite the cabin being metallic does it actually introduce an earth potential into the installation or are you just being cautious?
Will this fall under section 704?
Is this a construction site as administrative offices,toilets and canteens are not in the scope of section 704 and only the relevant parts 1-6 of bs7671 need to be applied
 
Agree,worried about the Main bonding conductors,the size is 50 mm.
This Swa will not provide that to the cabin.
The cabin is external,it’s a new cabin on a recycling plant.
Thanks.
 
I would tt it to be honest better safe than sorry also I wouldn’t be to worried about catenary wire if it is fixed to anything other than metal the supply side
 
Yes,if tt system used,will it import Tncs from the metalclad building,of the structure,which will be bonded to the Tncs system.
Will the caternary need to be isolated or ignore
 

Reply to Extraneous conductive bits & pieces in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

During an EICR I have found an isolator with no cpc present bolted to a large metal post and all the motorized metal car park gate, the fact that...
Replies
22
Views
3K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
I have just put in a sub distribution board in the middle of a field for a new supply for some poly tunnels (soil heating mats and lighting). I...
Replies
41
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock