cliffed

-
Arms
metallic portacabin used for offices,Swa is on a steel caternary,enters office to Rcd DB.
No separation of swa earth Tncs @ cabin.
I want to Tt it,what’s your thinking of caternary wire,it comes from building to cabin.
Will this still import Tncs,& will it also need isolation from cabin,where it’s fixed,obviously to the steel cabin.
 
Despite the cabin being metallic does it actually introduce an earth potential into the installation or are you just being cautious?
Will this fall under section 704?
Is this a construction site as administrative offices,toilets and canteens are not in the scope of section 704 and only the relevant parts 1-6 of bs7671 need to be applied
 
Agree,worried about the Main bonding conductors,the size is 50 mm.
This Swa will not provide that to the cabin.
The cabin is external,it’s a new cabin on a recycling plant.
Thanks.
 
Yes,if tt system used,will it import Tncs from the metalclad building,of the structure,which will be bonded to the Tncs system.
Will the caternary need to be isolated or ignore
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Extraneous conductive bits & pieces
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
cliffed,
Last reply from
cliffed,
Replies
6
Views
1,222

Advert

Back
Top