Discuss Bonding extraneous parts in the UK Electrical Forum area at ElectriciansForums.net
What about unistrut?To be an extraneous conductive part the metalwork has to be capable of introducing a potential into the Building. Unless the hand rail is connected in some way to structural steelwork of similar this is unlikely. We then call it isolated unearthed metalwork. Check the regs. there is a specific ohmic value to exceed for it to require bonding.
Thanks for you replies it’s hard to refer to the regs as it’s on machinery and plant. I know there’s a separate regs but not too sure on what they state. As far as I know BS7671 covers us to the isolater. Just wasn’t sure if I got a low reading it I could bond straight if the cable try to the extraneous part as the cable tray will be bonded back to the panel and then back through the supply to the MCC.From memory if its above 22k then you are unlikely to get any serious risk (even if you+MET go to 230V you would see no more than 10mA assuming human body as 1k), also if below 0.05 ohms (and an allowance for X meters of 10mm cable) it is already well-bonded.
Small stuff and support stuff like Unistrut, etc, that measures such that bonding is reasonably required you should also use your judgement: Is it likely to be touchable and the person simultaneously in contact with anything else? Is it used for something that might fail to make it live? Is there any part that someone might grab and, due to shock current, be unable to release?
In terms of bonding to nearby metal (instead of all the way back to the MET) then it certainly serves the purpose of maintaining equipotential regions, but you should check how well bonded that metalwork is back to the MET and what sort of CSA is used to see if any likely fault current can be handled.
Usually for external extraneous parts like pipes, structural steel, etc, you have the requirement for large conductors of the 10mm and above size (especially for TN-C-S) as you could see sustained fault currents in the many tens of amps range, but for internal hand rails, etc, that is unlikely so the sort of size used for CPCs would be reasonable.
Again the resistance test will tell you something about this. For example, if the handrail is showing 1k then you are unlikely to see high currents no matter what so, say, 4mm bonding of related metal via CPC or similar is fine, but if it is a couple of ohms then you might see hundred amp sort of faults and should treat it as you would for extraneous pipes, etc.
But don't believe me - get a copy of Guidance Notes 8 and read that!
Why’s it double the fault current?I don't know what the other regs might be or say, but electricity is basically the same before and after the isolator switch!
Check the resistance to earth of the item(s) and look to find out the CPC cable size all the way back to the MET. If it appears that all of the CPC is easily able to handle at least double the fault current the resistance would suggest, and it is physically robust (another reason the wiring regs has minimum sizes for bonding), then doing it that way ought to be OK.