During an EICR I have come across a metal tap and copper pipes supplied by a blue plastic pipe.

This measures 0.022 MegOhms, this is directly under the consumer unit which is metal.

Is this an extranous conductive part?
Extranous conductive parts Screenshot_20230601_094140_Gallery - EletriciansForums.net
 

Attachments

  • Extranous conductive parts Screenshot_20230601_094135_Gallery - EletriciansForums.net
    Screenshot_20230601_094135_Gallery.jpg
    180.8 KB · Views: 35
  • Extranous conductive parts Screenshot_20230601_094129_Gallery - EletriciansForums.net
    Screenshot_20230601_094129_Gallery.jpg
    188.5 KB · Views: 32

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,294
Well that's an unfortunate figure to get!!

Smack on the limit of what is classed as an extraneous conductive part (ECP)

I believe the resistance to earth of the suspected extraneous conductive part should actually be greater than 22K ohms between the suspected ECP and the MET of the CU (or nearest known verified connection to earth) (i.e 0.022M ohms), therefore yes, it is an ECP. Also, from certain literature I've read you could add on a factor of safety, bringing the value up to perhaps 25K, meaning your suspected part is definitely ECP.

It's a bit odd how it can test as low as 22K though, as you can clearly see both pipes being fed by plastic. Are there any other metal pipes coming off from those pipes, perhaps going straight into the wall, maybe hidden behind the insulation of the pipes?

Also, I cant see where your leads are attached to. What have you got the 2 leads attached to? Just noticed you say one end is attached to the CU. If the Cu is painted or has some kind of coating, this will affect the result drastically. I'd be opening the CU up and attaching to the MET (as long as you are an electrician).
 
Last edited:

Marvo

-
Staff member
Mod
Mentor
Esteemed
Supporter
Reaction score
10,078
I'm guessing you used a megger tester to get that reading? Most normal testers would have given you the result in ohms or kiloohms, not as a fraction of a megaohm ..... If you did then do the test again using a multimeter.
 

timhoward

-
Esteemed
Arms
Reaction score
7,872
t's a bit odd how it can test as low as 22K though, as you can clearly see both pipes being fed by plastic. Are there any other metal pipes coming off from those pipes, perhaps going straight into the wall, maybe hidden behind the insulation of the pipes?
THIS ^^^^
I'd be looking at that and thinking "How?!"

(a very idle thought - has the left hand screw for the tap grazed a cable?!)
I'm guessing you used a megger tester to get that reading? Most normal testers would have given you the result in ohms or kiloohms, not as a fraction of a megaohm ..... If you did then do the test again using a multimeter.
He did the right test, detailed in Guidance Note 8.
 

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,294
Thinking outside the box...

Perhaps it's the actual water that's causing the low resistivity?

Here's an extract detailing what cat 5 water may contain..

"Fluid category 5 (CAT 5) is described as a fluid representing a serious health hazard because of the concentration of pathogenic organisms, radioactive or very toxic substances. This includes any fluid which contains faecal material or other human waste, butchery or other animal waste, or pathogens from any other source."

Unfiltered tap water has a resistivity of between 1000ohms and 5000ohms (I think per meter). Dirty river water as low as 200ohms per meter (all found from the net, I'm not pretending I know this). So, I expect the resistivity of the cat 5 water is pretty low.

If the cat 5 water comes from another pipe nearby that is earthed, this may be the cause of the low IR reading. Very much on thin ice here though and I don't really understand all the implications. Interesting though.
 

timhoward

-
Esteemed
Arms
Reaction score
7,872
I'm sure John Ward did a video once testing water as a conductor and I remember it being surprisingly poor, but don't remember exactly to what degree.
 
Reaction score
13
Someone who actually knows what they’re doing.

The amount of sparks I know that assume plastic pipe = doesn’t need bonding, just because it says in the regs. You should always test the pipes because you can’t guarantee that they don’t shoot back into the ground within the installation
 

Reply to Extranous conductive parts in the Electrical Forum area at ElectriciansForums.net

Similar Threads

During an EICR I have found an isolator with no cpc present bolted to a large metal post and all the motorized metal car park gate, the fact that...
Replies
22
Views
2K
So to try & keep confidentiality, a broad question without specifics; A manufactured bed, mechanically operated by electrically powered motors...
Replies
6
Views
541
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
583
in the old bpg4 it stated Absence of supplementary bonding for installed Class II equipment where required (such as in a location containing a...
Replies
1
Views
859
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
508
Advertise Here

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top