I've relooked at the site I was getting my figures, It's a little confusing, but It looks like the 1000ohms - 5000ohms for unfiltered tap water may be per cm as you suggest. This would then fit in with JW's video as well. thanks for pointing that out LMO.
 
  • Like
Reactions: DPG
imagine most Sparks doing a test to prove its ECP especially in the newer build houses where plastic cold piping enters the house, I doubt it.
This is one reason why we use to install a MBPC to gas water etc BELT & BRACES
If the resistivity of tap water is 1000ohms p/cm (worst case) then I cant really see it being a problem in a domestic house. You would somehow have to have something that had almost direct continuity (downstream) with the MET and the water within 22cm's of the plastic pipe connection.

Now with the OP's example, the resistivity may be around 200ohms p/cm. meaning the 22cm's jumps to around 1meter. Possible that those plastic pipes become metal in the box they are hidden in and have a very good connection to earth. Still seems unlikely though.

I really want to know how the OP gets a figure of 0.22Mohms now!!? OP, could you please dismantle the box and dig up a section of earth and concrete floor please, down to depth of 1.1m? :)
 
  • Like
Reactions: timhoward and DPG
I've relooked at the site I was getting my figures, It's a little confusing,
Confusing sums it up well.I looked up several sites and quite frankly you could make an arguement for either case.But the advantage of discussing "tap water" is that we all have easy access to it.I myself have taken my own IR tester to it on several occasions over the years and my readings were somewhat similar to J.W.,s (give or take a few thousand ohms)
 
If the resistivity of tap water is 1000ohms p/cm (worst case) then I cant really see it being a problem in a domestic house.
correct.It is,nt.
You would somehow have to have something that had almost direct continuity (downstream) with the MET and the water within 22cm's of the plastic pipe connection.
I think the issue may lie with the "Cat 5" label.That is as far away from tap water as you can get.
Bearing in mind that the resistivity of water drops considerably when pollutants are introduced to it ,that would be my first area for investigation.
Is it actually allowed to have a "Cat 5" tap in a domestic scenario in the UK?
 
I think it’s fed from a tank in the open loft area (no ceiling) of the bin store so it’s likely full of dead flys and whatever , why this was done I have no idea , I’m not sure if the tank is fed by mains water .
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

newfutile

Arms
Supporter
~
Joined
Location
hemel hempstead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Extranous conductive parts
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
newfutile,
Last reply from
newfutile,
Replies
24
Views
4,046

Advert