Discuss Extranous conductive parts in the UK Electrical Forum area at ElectriciansForums.net

I've relooked at the site I was getting my figures, It's a little confusing, but It looks like the 1000ohms - 5000ohms for unfiltered tap water may be per cm as you suggest. This would then fit in with JW's video as well. thanks for pointing that out LMO.
 
imagine most Sparks doing a test to prove its ECP especially in the newer build houses where plastic cold piping enters the house, I doubt it.
This is one reason why we use to install a MBPC to gas water etc BELT & BRACES
If the resistivity of tap water is 1000ohms p/cm (worst case) then I cant really see it being a problem in a domestic house. You would somehow have to have something that had almost direct continuity (downstream) with the MET and the water within 22cm's of the plastic pipe connection.

Now with the OP's example, the resistivity may be around 200ohms p/cm. meaning the 22cm's jumps to around 1meter. Possible that those plastic pipes become metal in the box they are hidden in and have a very good connection to earth. Still seems unlikely though.

I really want to know how the OP gets a figure of 0.22Mohms now!!? OP, could you please dismantle the box and dig up a section of earth and concrete floor please, down to depth of 1.1m? :)
 
I've relooked at the site I was getting my figures, It's a little confusing,
Confusing sums it up well.I looked up several sites and quite frankly you could make an arguement for either case.But the advantage of discussing "tap water" is that we all have easy access to it.I myself have taken my own IR tester to it on several occasions over the years and my readings were somewhat similar to J.W.,s (give or take a few thousand ohms)
 
If the resistivity of tap water is 1000ohms p/cm (worst case) then I cant really see it being a problem in a domestic house.
correct.It is,nt.
You would somehow have to have something that had almost direct continuity (downstream) with the MET and the water within 22cm's of the plastic pipe connection.
I think the issue may lie with the "Cat 5" label.That is as far away from tap water as you can get.
Bearing in mind that the resistivity of water drops considerably when pollutants are introduced to it ,that would be my first area for investigation.
Is it actually allowed to have a "Cat 5" tap in a domestic scenario in the UK?
 
I think it’s fed from a tank in the open loft area (no ceiling) of the bin store so it’s likely full of dead flys and whatever , why this was done I have no idea , I’m not sure if the tank is fed by mains water .
 

Reply to Extranous conductive parts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

During an EICR I have found an isolator with no cpc present bolted to a large metal post and all the motorized metal car park gate, the fact that...
Replies
22
Views
3K
As above the chest level from ground ,metal ANPR housing has no connection to earth ,it has monitors modems and a camera inside with a 230 volt...
Replies
2
Views
649
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
492

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock