No amount of calibration supercedes the laws of physics, 0.00 ohms is impossible under normal conditions and any even vaguely competent electrician will understand this.
I think we all understand this so what is the solution. Calculating the value would not be acceptable as it has not been proved by a test. Testers we use day to day do not verify such low resistances and those that can do not deliver a 200ma test current as required by BS7671.
 
Only a test can prove your calculation and it is a schedule of TEST results.
I agree except seeing "0.0" makes one have to look into it, seeing 0.002 as a calculation against it gives the instant solution and additionally shows the author has thought about the apparent confussion.
 
I agree except seeing "0.0" makes one have to look into it, seeing 0.002 as a calculation against it gives the instant solution and additionally shows the author has thought about the apparent confussion.
It is all very well put a calculated figure down but how do you know the installed conductors actually tally with that calculation?
 
It is all very well put a calculated figure down but how do you know the installed conductors actually tally with that calculation?
Because you've done a measurement and the reading (0.0) tallies with what you'd expect for that scale of resistance (0.002) and the resolution of the instrument.
What you don't know is whether the actual is (say) 0.003 instead of 0.002, but does it matter ?
 