Hi guys,

Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms.

Called the network and they said they would send a guy around who promptly turned up and checked.

However his tester was giving a reading of 0.30!

I checked again using the same method he did and still got 0.44.

He said that he has found that some multi testers use the wrong range and we should be testing with a 20 ohm range and not 200 which apparently they are set at by default as otherwise it could be difficult to get a reading from a tt installation?

Anyone else had this?

I have dug out an old robin 4120dl that I used to use and that is still set at 20 ohm range from when I used to use it.

Might give that a hi in my place and compare but has anyone else had this?
 
Discrepancy between meters? ........... all the time!

and often with recently issued certificates of calibration. I'm not sure if supplied leads are tested or whether calibration takes place on meter only, but I've seen meters come back from calibration when I know for a fact the leads on the meter are dodgy.
 
and often with recently issued certificates of calibration. I'm not sure if supplied leads are tested or whether calibration takes place on meter only, but I've seen meters come back from calibration when I know for a fact the leads on the meter are dodgy.

I would expect only the meter to be calibrated.
 
Ok so just done a quick test on mine.

Megger mft on high gives 0.30
Robin 4120dl on 20ohm hives 0.22
Robin 4120 on 200ohm gives 0.28

Bearing in mind these readings are supposed to be what we should record and work to on installstions if we get a reading over max ze and yet on another tester it can be well below, what are we supposed to do?

This potentially screws up perfectly acceptable readings and modifications to circuits to bring them in line for no reason at all.

As far as the DNO are concerned their network is well within the max allowable.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Odd PME discovery?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Thread Tags

Tags Tags
pme

Advert

Thread statistics

Created
Initforthemoney,
Last reply from
Initforthemoney,
Replies
5
Views
839

Advert

Back
Top