Got a call out to a job, drainage company had plugged a socket tester in and said to client there was an issue and they couldn’t do the work until it was resolved. Plugged my martindale in and everything seemed fine. Done a ZsRCD on the sockets and was getting 4.21 ohms, done a ZsRCD on cooker circuit and was getting a very high reading also. Tested the upstairs sockets which was on the other rcd and got a very high reading also. When doing a ze at the db I got 0.05, and my r1+r2 for the socket circuit was 0.28 ohms. Checked all connection within consumer unit and all very tight, even tried swapping over the neutral going from main switch load to the neutral bar and no change. Now when I do a zline test on these circuits I got 0.19 for the cooker and 0.48 for the sockets. It’s a metrel test kit I was using that’s why I was doing a ZsRCD test as to not trip rcd, anybody any ideas?? I know it’s a long post, rcd tripped within the times required also. Only thing I didn’t rule out which I thought of after was maybe the main switch neutral side starting to go faulty? Hence the high reading, didn’t think to check that at the time but