Hi all
Still got a hangover from saturday but im struggling with one 🤣

EICR, everything tests ok until i press the button on the RCD and it doesnt trip.

Tried 2 spare RCDs same thing.

When i disconnect the sockets Neutral from the busbar it then works.

Type AC 30ma 80A RCD

What am I missing?

Thanks in adavance
Mick
 
Is there a fault on that circuit?
 
  • Like
Reactions: DPG
Is the IR N to Cpc definitely OK.

Is it only the socket (i assume ring final) circuit that allows the rcd to trip when disconnected.
 
Last edited:
Is the IR N to Cpc definitely OK.

Is it only the socket (i assume ring final) circuit that allows the rcd to trip when disconnected.
Yeh when i disconnect the neutrals at the DB for the socket ring, the button works

IR is clear on all circuits
 
Yeh when i disconnect the neutrals at the DB for the socket ring, the button works

IR is clear on all circuits
Are the CPC's connected to the Protective Earth or disconnected from the terminal during the IR test between Live conductors and Earth?
 
  • Like
Reactions: westward10
It is the most common cause a neutral to earth fault. Have you removed anything plugged into the circuit?
 
  • Like
Reactions: Tom256
It is the most common cause a neutral to earth fault. Have you removed anything plugged into the circuit?
Empty house nothing plugged in,

IR the sockets in question seperate after rcd wont trip. All clear
 
As in #6 are you leaving the cpcs connected when testing.
 
No i removed and tested after rcd test button wouldnt work
The IR test is done with the CPC's in the Earth Terminal.
 
  • Agree
Reactions: westward10
No i removed and tested after rcd test button wouldnt work
What earthing system is it ?

If it definitely is the ring final, I would be disconnecting/splitting it to see if I could narrow it down.
 
Last edited:
What earthing system is it ?

If it definitely is the ring final, I would be disconnecting/splitting it to see if I could narrow it down.
As soon at the neutrals are disconnected the button works

TNS earthing system

Im going back tomorrow morning see if can solve it
 
As soon at the neutrals are disconnected the button works

TNS earthing system

Im going back tomorrow morning see if can solve it
Can you temporarily wire in a rcbo to the ring final and see if that fails to trip ?
 
Redo the IR but leave the cpcs connected. As already mentioned never disconnect cpcs to carry out an IR test.
 
Redo the IR but leave the cpcs connected. As already mentioned never disconnect cpcs to carry out an IR test.
I done it connected 1st then removed them to test just that circuit
 
I done it connected 1st then removed them to test just that circuit

Just a thought but are your spare RCD's Brand New?

https://engx.----------/f/wiring-and-regulations/28594/cause-of-rcd-not-tripping-with-test-switch

The above was posted 3 years ago and they had the same problem turns out all 3 RCDs were faulty

They were second hand parts from a specialised supplier because new parts were not available but you may have the same issue?
 
Just a thought but are your spare RCD's Brand New?


The above was posted 3 years ago and they had the same problem turns out all 3 RCDs were faulty

They were second hand parts from a specialised supplier because new parts were not available but you may have the same issue?
Yeh mate they were brand new, i changed the sockets in the lounge and it started working, strange because everything tested out ok before and after changing sockets
 
  • Like
Reactions: PS Electrics
Yeh mate they were brand new, i changed the sockets in the lounge and it started working, strange because everything tested out ok before and after changing sockets
Argh....!
We need IR figures, not 'it tests ok'.
Now we're all thinking 'I bet there was a N-E fault. 😅
 
  • Like
Reactions: DPG and James
Argh....!
We need IR figures, not 'it tests ok'.
Now we're all thinking 'I bet there was a N-E fault. 😅
It was >999 on all, tested cables connected and individually, he ce the reason i came on here to ask for ideas
 
  • Like
Reactions: HappyHippyDad

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Glasgow
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Heavily Qualified Electrician / Teacher / Tutor - etc

Thread Information

Title
EICR - RCD Wont trip on test button
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
mbu2ns,
Last reply from
mbu2ns,
Replies
19
Views
1,463

Advert